1.5kW motor may start with 13A it could also trip. Theory says 16A blue sockets but in practice a B16 MCB will likely trip before a 13A fuse. Which means a C16 MCB and this will trip with the same instant current as a B32 MCB but with a welder it depends how much welding is done.
As to a B40 supplying whole shed yes it would be my aim to have a larger MCB in the house to any MCB in the out building even if some times the house may trip first.
So if going for a 40A MCB in house then 6mm SWA and 10mm T&E is the minimum size and assuming a B40 then loop impedance of 1.15Ω to satisfy that you need to know value in the house.
For lighting to comply with 6mm cable max length around 21.5 meters assuming incoming at 0.35Ω the destination should be around 0.52 Ω if going for power only then should be OK for around 37 meters and the destination impedance around the 0.64 Ω mark. A type C40 MCB is requiring 0.57 Ω impedance so cable length 31 meters.
Can't remember how far you said it was jump to 10mm and limit is 54 meters. Remember I am assuming at the house consumer unit reading is 0.35 Ω or better. I have also taken into account correction figures. Working on installation method C.
I would be wary of going to the limits. You clearly want it to pass. As to lights using LED or HF florescent unlikely to be a problem even if volt drop not complied with.
As to a B40 supplying whole shed yes it would be my aim to have a larger MCB in the house to any MCB in the out building even if some times the house may trip first.
So if going for a 40A MCB in house then 6mm SWA and 10mm T&E is the minimum size and assuming a B40 then loop impedance of 1.15Ω to satisfy that you need to know value in the house.
For lighting to comply with 6mm cable max length around 21.5 meters assuming incoming at 0.35Ω the destination should be around 0.52 Ω if going for power only then should be OK for around 37 meters and the destination impedance around the 0.64 Ω mark. A type C40 MCB is requiring 0.57 Ω impedance so cable length 31 meters.
Can't remember how far you said it was jump to 10mm and limit is 54 meters. Remember I am assuming at the house consumer unit reading is 0.35 Ω or better. I have also taken into account correction figures. Working on installation method C.
I would be wary of going to the limits. You clearly want it to pass. As to lights using LED or HF florescent unlikely to be a problem even if volt drop not complied with.