Electric cooker must fitted to a 30a/45a circuit connected staight to distribution board.6mm tw&E cable terminated in a BS4343 30a socket positioned near the cooker for easy access.The cooker can then be isolated locally for safety/maintenance.
A cooker circuit of 30a using 6mm csa cable and a 30a socket,protected by a 30a mcb will suffice.The 30a socket is placed near to the cooker,so that the cooker can be isolated.The socket can be under worktop,but it must be easily accessible.
The diversity applicable to the current demand for a cooker makes a 30a circuit suitable and will provide the best protection for it.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local