oven to work of 2.5 ring main
6 Apr 2008
Yorkshire
are there any ovens which will work off a 2.5 ring main?
or will i have to run in a new 6mm cable.
thanks
There is a oven/ring unit called the Baby Belling designed to be plugged into a 13 amp outlet but Appendix 15 BS7671:2008 recommends connecting cookers, ovens and hobs with a ratted power exceeding 2kW on their own dedicated radial circuit. To avoid overload of the ring circuit.
Eric
if its just an oven (no hob) then most come with a plug to put straight in, so if you already have a socket there and you dont need an electric hob (gas is generally far better) then your all set (assuming the circuit there is as it 'should be'.
if your designing/ installing the circuit then, as stated, above there is now a regulation regarding >2kw (fixed? constant?) loads not been on the ring, I didnt think it specifically mentions ovens (or if the OSG gives more guidance) and I'm not sure which specific loads it refers to as things like the tumble drier, washing machine, kettle, toaster hairdryer tend to sit in the same socket pulling that sort of power. Of course if your putting in the circuit there are all the other regulations to cover, including everyone’s favorite part P.
Cookers, ovens and hobs are specifically mentioned.
Have a look at Appendix 15.
thanks for the clarification (I dont have a copy). so it comes down to: are you putting a new socket/connection point in? or plugging it in to an existing one?
If you read 433.1.5, it suggests that one way of relieving loads on a ring final could be putting cookers etc of more than 2KW on their own radial.
From my reading, it does not make it mandatory to run a separate radial evrytime a 2KW+ cooker has to be connected. Its a suggestion, nothing more.
TTC, I agree, it's not mandatory though it helps with compliance and would be good practice.
I've never liked the idea of plugging ovens into a downstairs ring final.