UPS and the regs
1) Whole idea of a UPS is to be uninterruptible so fitting a RCD on the output seems to defeat the purpose. I would consider if it uses a socket outlet under 20A then 411.3.3 applies and 13A sockets should have RCD’s unless specific labelled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.
2) Earth connection I would consider that a PEN conductor should never be used with a UPS as if the supply cable is cut it could lose the earth connection without losing the supply. 418.3.5 requires an earth.
3) Since it is designed to be uninterruptible should RCM’s be used?
4) 430.3 says there must be a protective device but where the design is so that overload will cause the unit to crowbar into a safe state is this enough?
5) 433.3.3 does refer to conditions where overloads may be omitted. But the list doe not include servers etc. May be if powering telephones than these may be considered safety equipment.
My own thoughts are where there is a single output from a UPS then like with the bathroom transformer there is no real danger as if the line was to connect to earth then it would still not give anyone a shock.
However where the UPS has multi outputs supplying more than one item then it should have a RCD and it’s own independent earth system which does not rely on the supply authorities earth.
I also would consider an earth rod is an extraneous-conductive-part when the supply authorities earth is connected and can be connected at all times.
The large servers are not really a problem having no RCD (in own locked room) and only the provision of independent earth may be an issue but often they have that anyway and call it a clean earth.
But on the smaller scale with an UPS under the desk powering computer, printer, monitor etc. Then I can see a problem. The RCD should not really be an issue as it should never trip unless there is a fault but ensuring that the UPS earth connection is never compromised is another thing and how one can ensure they are only used with sockets where there is a permanent earth independent of supply authorities earth I don’t know? Maybe Walsall Gauge plug and sockets.
I would like to hear what is done in practice. And what other think about what we should allow? I am not sure how earthing and RCD’s should be used on this one. The question came to light while fitting a 3KVA unit on a boat where we used the hull as an earth and used only a single Class II charger with no earth connected to shore power. No earth is connected between shore and the boat. The jetty is all wood and the 16A outlets are all plastic so the only way one could get a shock is from neighbours boat if they have earth connected. BS7671 does not apply and due to size of boat neither does RCD (Recreational Craft Directive). But my son compared the setup to an UPS and that got us thinking. If we wanted to do same with a caravan what would the rules be then? And with solar panels inverters on caravans are getting more popular. I have not seen a single caravan with a earth rod connected! Even when they have a generator. Although I have seen greasy spoon cafes on side of the road with rod next to generator.