Thanks Matt.
Thats a brilliant way of explaining it to my boss tomorrow.
I see your reasoning behind the vacuum pulling and the pressure pushing also.
Thanks mate.
no problem mate, I think its probably the manufacturers prefered way of testing as it also tests the integrity of the loading spring and its a smaller vacuum pressure incomparison because it is pulling the seal off its seat, I wouldn't worry too much as they will know the specs
on another note (same theme) and sorry for hijacking your post just out of curiousity since you obviously do a lot of work on these.....
last week I had to change a flygt 4Kw borehole pump and it failed after a day
I was onsite to fit a low level float to the storage tanks and also noticed the panel PLC was reporting borehole pump 1 O/L had tripped so metered it out and found it had an O/C winding.
they had a spare one onsite (new but unpackaged and lying in a store room for around 5yrs) so went next day to change it (matter of urgency as its a busy hotel/complex and all their water comes out the ground) got the old one out and the new one in and because they have no level sensors in the boreholes
and also because the FLYGT doesn't have any internal protection
I measured the water table at borehole 1 because I was worried incase the pump had ran dry
the pump was at a depth of 52.2 metres and the water table was at 45.3M pumps off but fell to 49 metres with both pumps running. so really only about 3 metres of head at the pump. anyway because the hotel needs both pumps running to cope with demand I put it in service as I was going back in the morning to measure up to quote for borehole level sensors etc.
got there next day to find the whole plant had tripped out on the main RCD (a bit more work req to sort out discrimination too) and of course found that the culprit was said pump.measured the windings which were ok on continuity but now leaking to earth (0.034 Mohms)
this was friday and haven't been back yet to pull it out or re-measure leakage but what do you reckon on cause
1)moisture ingress due to damage to the case/cable because it was lying unpackaged buried under crap etc for 5 yrs?
2)damage to the machanical seal because of above? or
3)damage because of dry running?(only 3 metres at most of head)
cheers for any input
Matt