https://www.diynot.com/forums/viewtopic.php?t=246442
10 Jul 2004
Looking on page 28 far right paragraph, I am having trouble understanding how it says " if the boiler is supplied by 28mm pipe, runs 1-2 2-4 and 22mm tube for 4-6 the re-worked pressure drops are 0.18 + 0.13 + 0.17 =0.48mb" I am not seeing this on the chart, am I missing something ?
Not sure what you're asking ped, and the link only takes you back to the same page.
If you want to discuss gas pressure send me an email.
That makes sense.
1-2 has to take the total load of 3-5-6.
2-4 has to take the load of 4-5.
4-6 has to take the load at 6.
Ss what you mean, there's a few errors in the chart and the para :shock:
Are you happy with that or do you want me to work out what they should be.
No thats fine, I can work it out thanks, but one question, Kw divided by 38.5Mj/m3 then x by 3.6, what is the 3.6 relating to ?
I think you are mis-reading it.
To determine the gas-rate for an appliance divide the appliance heat input in kW by the ‘calorific value’ (CV) of the gas being burnt. In the case of natural gas this is 38.5MJ/m3.
For example, for a 10kW appliance the flow rate will be: 10 ÷ 38.5 = 0.26 litres/second.
This figure can then be multiplied by 3.6 to convert the flow rate from l/s to m3/hour = 0.26 x 3.6 = 0.936m3/hour.
So the 3.6 converts from litres per second to cubic metres per hour. 3600 seconds = 1 hour; 1000 litres = 1 cubic metre; 3600/1000 = 3.6.
No thats fine, I can work it out thanks, but one question, Kw divided by 38.5Mj/m³ then x by 3.6. what is the 3.6 relating to ?
It does explain where it comes from.
To determine the gas-rate for an appliance divide the appliance heat input in kW by the ‘calorific value’ (CV) of the gas being burnt. In the case of natural gas this is 38.5MJ/m³.
This figure can then be multiplied by 3.6 to convert the flow rate from l/s to m³/hour = 0.26 x 3.6 = 0.936m³/hour.