Boiler under gassed - AT RISK
24 Nov 2010
London
I had a Valliant ECOTEC 831 boiler installed 2 years ago. At the 1 year service the boiler man said the appliance was under gassed. The pressure at the meter was 20.4mb but when all appliances (I also have a gas hob) are in operation the pressure at the boiler is 14mb.
The boiler guy put an AT RISK notice on the boiler and turned it off.
He said I should increase the size of the pipes, the problem is that the boiler is quite far from the meter and runs almost exclusively underground or under the floor. There is a small section exposed about halfway between the meter and the boiler so at best I can 'easily' replace about 2-3 meters. But I am not sure this will help much.
Looking at the commissioning checklist the engineer noted the gas rate was 3.18. Where it refers to pressure he made a note (which I can't quite make out) that looks like it says F/SET or P/SET but he didn't record the pressure.
I have a few questions and hope you guys can help me.
1. Is it illegal to continue using the boiler if it is AT RISK?
2. Should the engineer that installed the boiler have checked (and fixed) the gas supply? If so do I have any legal recourse?
3. Is there anything else I can do that would avoid me having to rip up the floor boards to replace the pipes?
Thanks!
If it's not affecting the boiler i.e fga tests ok it should be ncs
Thanks!
No its not illegal to use, which is why the boiler is only turned off by the controls but its not advised to use.
The engineer should have installed it leaving a 1mb drop. He should have sorted that from the start.
If you have a wall the a gas pipe can be run externally, then you can do that otherwise there is no other option sadly
You hardly need to 'rip' the floorboards up as they were taken up when the pipe was installed. Not a big job then is it?
There is an external wall that can connect the meter and the boiler. I wasn't sure if you could have it running against a wall or if it had to be covered?
Any idea how much it would cost to have that done?
I don't follow. Only the boiler was replace and attached to the existing pipes. since the pipes were installed the bathroom has been tiled so I would think it would be a big job.
what are the kw ratings and Co2 readings from the engineer that turned it off?
Oh sorry. My crystal ball is broken.
OP look he has turned it off because its not right, ring an RGI or the installer an advise them. the installer will just say it was ok when i tested it!! good luk :wink:
that only depends if it does not effect the hob flame picture when it fires up, if it does id class it as ID
The guy checked the hob flames and they didn't show any effect when the boiled fired up. I remember because he said at the time if they did he would have to disconnect it.
Does that make it At Risk or Not up to current standards then?
if it was me i would say ncs if all checks are ok and NOT affecting other appliances