G
GaytonTonner
As Doitall wrote, you do not have a low-loss header, it is a reverse return. Well it looks that way from the picture.
Your prime problem is preventing heat exchanger cracks. First find out what the delta T (temperature differential between F & R) is. If it is say, 20C, then determine the flow temperature and fit a blending valve on the common return to the boilers. Set this at 20C below the setpoint of the boilers. If the boilers setpoint is say 75C, then set the blending valve to 55C. This ensures that the return temperature does not fall, below 55C. Too wide a Deta T can crack the heat exchangers, as you know. Then the boilers are operating with their comfort range.
The blending valve is giving back-end protection. This was to stop non-condensing boilers condensing and rotting the insides of boiler burner boxes. In your case it is to stop heat X cracks.
If you set the boiler to say 75C, 75C will enter the cylinder coil giving a quick warm up, yet the return temperature will not be say 30C. The boilers cycle on themselves partially. They fully cycle on themselves on cold start until above 55C return. The valve slowly opens sending water to the cylinder/CH circuit keeping the boilers Delta T in check.