I'm getting very confused, since this is the second time in this thread you have suggested that I have used the wrong Table or read the wrong CCC. I clearly need some help.There is no tabulated rating of 38A.What intrigues me is where the 35A figure came from. Even if the installation were Method B, the tabulated CCC of a 6mm² cable would appear to be 38A.
All evidence points to the cable being laid in the floor void and therefore will not be clipped direct.
What evidence ?
Read my previous response (5.15) to you or the opening post.
What CCC does your BRB give in Table 4D2A for 6mm² cable, Reference Method B, "1 two core cable, single phase a.c. or d.c." (i.e.column 4)? ... or do you think that is the wrong Table to be using? Conversely,where is the 35A figure tabulated?
Thanks for your help.
Kind Regards, John.
That certainly gives 35A, but why on earth would (s)he be assuming Reference Method 102 - which relates to a very specific situation (and one which we have not been given reason to believe would apply in this case)? In any event, I made it very clear that I was quote figures tabulated for Reference Method B.I think he may be referring to table 4D5 ref method 102.
But you three continue to say I am wrong based on your imaginations without looking at the facts presented. And most importantly creating the dangerous impression that this cable can be run at a dangerously high current.
Because of the installation method, the 6mm cable will have a maximum rating of about 35A, so you are stuck with the 30A fuse.
FFS, read the opening post, which clearly demonstrates that the cable is not clipped direct. Or is the problem that you don't like evidence that contradicts you're irresponsible and dangerous advice?