my system doesn't need or want a by pass. Balls to part L. Written by monkeys.
I wasn't suggesting that it should be 'blasting out heat all the time'. It only heats when the heating is on, and this will be properly controlled with weather compensation.
The Vitodens 200-W becomes a six-pipe boiler when it is fitted with a Sub Mounting Kit with Mixer [this only works with weather compensation].
Otherwise, it is a four pipe - there is an on-board diverter valve.
The Domestic Building Compliance Guide (October 2010) makes it clear that a bypass is only required if the boiler manufacturer's instructions so advise. In which case, it must be an auto bypass.Properly set a pressure sensitive auto bypass [now required by part L] will only really allow bypass in a correctly working system at this phase of boiler operation.
I often wonder why so few manufacturers make boilers which modulate below 5kW. Modern houses are very well insulated and will only need about 7 or 8 kW to heat them in very cold weather, so logically the boiler should be modulating down to about 2kW.I have homed in on the Geminox 1 to 10kW boiler set to 40-45C or on a weather compensator only heating the UFH zones to eliminate a thermal store.
JonasX";p="2138021 said:"Smokebox, the problem of auto by-pass valves also hit me when looking at efficiencies of return temperatures. As you have pointed out, raising the return temperature can reduce efficiency greatly. Using a weather compensator ensures the return temperature is as low as possible enhancing efficiency. WC does not prevent the return temperature rising greatly when an auto by-pass valve opens. "
Jonas - thanks for comments and new and useful thoughts (new to me anyway!
I'm glad you see and agree that minimisation of wasteful bypass is essential to maximising condensation efficiency, which is the whole point of a condensing boiler! Some bypass must be provided just at flame extinction to prevent the numpty damage I suffered, or some other provision to quickly unload the heating coil at that point in time. The first time I had a bang, I truly though we had had a gas explosion! I think the thin narrow multiple tubed spiral exchanger used in the ecoTEC Plus series may be especially vulnerable with little room for sudden water vapour expansion from local 1000*C hot spots!
The weather compensator idea, amongst other things, in ordinary running will achieve return temps as low as computations will allow and this is good but I gather some people feel something is wrong if a rad doesn't feel obviously warm, though it may well be delivering sufficient low temp energy on only slightly cool days. Also the subjective feeling of "cosy comfort" may be missing. [As mentioned elsewhere I am aiming at the Vaillant system, and hope to discuss separately.]
It will not however help protect the expensive heat exchanger in the brief time after flame & zone shut down however. Something else needs to be provided.
The second link to a Grundfos PDF I provided earlier is a detailed technical one AND VERY MUCH WORTH LOOKING AT IN RELATION TO THE AUTO-ADAPT PUMPS.
I am interested to hear of the low power modulation possibilities of Geminox, and also of the heat storage buffer scheme. All that is really to do with be actually able to use Weather compensation in the modern well insulated rabbit hutches they build nowadays. Otherwise inefficient boiler boiler cycling is inevitable on slightly warm cool days!!
smokebox
I suspect it's psychological. Customers like radiators to feel hot when they touch them. If they are not, they immediately say: " No wonder I feel cold - the radiators are not on."
Did you find out the price of a Geminox boiler?
OP
I am impressed with your research and understanding of these aspects. I largely agree with the conclusions that you havce come to.
MM has given advice which is amusingly contrary to his employer's advice. He also specialises in his employer's boilers.
You seem to be lucky because your particular boiler model is very sensitive to a lack of flow through it. Consequently an ABV is usually required to prevent boiler problems which we see as caused by less than ideal software. on the system and combi versions it is not a problem and just on the heat only.
All the advice, CHESS, good practice etc. is that an ABV is fitted to all installations. Many installers now do this but there are still many who dont because they dont like paying the cost when their customer does not know that its required.
You should note that the smart pumps have not been very popular. Boiler makers have not used them and are trying to get more efficient pumps using permanent magnet motors. In due course those are likely to be used with the equivalent of an inverter drive. A very few makers use stepped output pumps but only 2 or 3 steps and not totally variable.
I have not studied smart pumps in any detail but they seem to be most effectively used as a constant head device. That does not solve the minimum flow rate through the boiler which is expected by its software.
Many installers familiar with the Vaillant 400 series problems take the view that with a 28 kW or larger model a more powerful pump is needed than the 15-60 series.
Your research has apparently not noted or heeded that the advice is to only allow 2 kW for water heating in addition to the heat loss of the house. This largely arises because the water heating should be started before the heating comes on in the morning when the whole boiler output will be available.
Congratulations on having such a well insulated house! But based on the info you have given your boiler is oversized and this compounds the minimum flow problems.
Tony Glazier
The boiler itself at full output flow of 1220 l/hr at 20*k flow return differential doing 30 kW has a high resistance of 2.4 metres on its own consuming a vast amount of pump energy just to get the water through the boiler!!
I have a growing uneasy feeling about persisting with a smart pump, but it should be doable. I am beginning to see why some fitters are cautious about them!
smokebox
Mysteryman has directed me to look at the Viessmann Vitodens 200-W with weather compensation. Does this really have six pipe connections, one pair each for the cyl, rads and UFH? It sounds like a normal boiler adapted using complex internal controls which will be expensive to replace when faulty.
It still only modulates down to pretty high kilowatt rate, unlike the Geminox's 1 kilowatt, so I would expect burner cycling from the Viessmann.
'tis why I don't fit Vaillant.
If you are concerned about HE strain have you not looked at thermal stores and LLH as alternatives?