I have had solar PV panels installed, and the installation was complete on October 21st. The panels are fixed on the roof, and I export the surplus. There is a generation meter, but no export meter.
The generation meter is a Landis & Gyr 5235A, and I also fitted one of these http://www.energymonitorworld.com/prod2.cfm?product=71698
On 7th November, the readings were:
Generation meter: 50 units
OWL meter: 51 units
Today the readings are:
Generation meter: 57 units
OWL meter: 63.6 units
So why is there an increasing discrepancy between the two? The weather has been a lot gloomier in the last 2 weeks, so the units per day figure is well down, but that ought to affect both meters the same (?)
I downloaded the L&G manual and found this. I'm no electrician, so I could do with a translation, but it seems to me to be relevant.
3.2 Anti-creep
Below starting current, the meter enters into an anti-creep mode. In this
state the metrology LED is permanently lit and the registers do not
increment. The LED remains lit until the meter current is increased in a
forward direction beyond the starting current. The starting current is shown in the technical summary.
The starting current is 0.4% of lb (whatever that means).
Is the L&G meter not recording all the current?
Is it "Working As Intended"?
I would appreciate any input.
OWL meter: 51 units
3.2 Anti-creep