M
mysteryman
Tony, as I explained above, on a water priority system you do NOT add any extra for DHW. The boiler will not do CH and DHW at the same time, so you size to the greater load, in this case the CH.
How big is your house??Here are the results of the calculator, I've broken them down;
Main House = 31.47kw
Granny annex = 12.55kw
Place your bets now people - 12 pages? Maybe 9....![]()
It's not 12-18 bedrooms but it is a large house.44 kW is a massive heating load. Is it really 12-18 bedrooms?
Are you paying about £3000-£5000 per annum for gas?
You should never size a boiler for an extension planned for a long time into the future as thats inefficient until the extension is built.
Tony
Thanks mate, I will list the information I put in below (was done in 4 seperate parts).If you will post the data you entered into the calculator, I can check if you have made any mistakes.
I made it 15.74kW. Probably a typo?Living Area
Dwelling Type: Detached
Boiler required = 15.47KW
Agreed. Better loft insulation would reduce it below 7.39kWLeisure Rooms
Dwelling Type: Detached? I think you mean semi-d? as there are only three external walls
Boiler required = 9.37KW
Agreed.Sun Lounge
Dwelling Type: Detached? 3 walls = semi d
Boiler required = 6.03KW
This will reduce to less than 27kW with better roof insulationMain House Total= 30.87KW
Granny Annexe
Atag Q38S
Vaillant EcoTec 46KW Commercial
Vaillant EcoTec Plus 37KW System
Viessmann Vitodens 200W 45KW Commercial
Broag Remeha Avanta Plus 39C (offer conversion to a system boiler)
Broag Remeha Quinta Pro 45
Could people offer comments on the above, with actual experience. Also open to other recommendations if you think there is better for the money.
Do people know the prices of the above boilers? Not RRP but the better deals
So you only have six inches or so between the tiles and the ceilings?Now I have some questions about fitting insulation. In the granny annex and Leisure rooms the ceilings are the type that run parallel to the roof (ie they are sort of a pitched ceiling), there is no access to lay down some more insulation.
As for the boiler, I have reservations about supplying everything from the one boiler. You don't say how far the granny annex is from the main house, but there could be a considerable heat loss in the pipes between the two buildings and control systems will get complicated with programmers and thermostats in the annex controlling a boiler in the main house. There is also the matter of supplying the annex with hot water.
Separate boilers is probably the better solution.
If that can be done easily, then it's worth doing.I could possibly lift the outside floor up and re-do the pipes with mega insulation round them.
You really need a motorized valve to close off the annex when it doesn't need to be heated. The valve could be in the main house, near the boiler, controlled by a wireless programmable thermostat from the annex.I generally wont be too fussed with thermostats in the annex and am sure the TRV's should be able to do all the temp adjusting we need. We don't use much heat in there really, only a couple of hours a day on low settings.
Four zones are possible (plus hot water) each zone would require a motorized valve to shut it off when heating is not required. Each zone would be controlled by a programmable thermostat. Depending on whether you want central control over times, there are several options available. Do a search for Honeywell Evohome.What I had in mind was sort of 4xZones for different times as we need diff areas on at different times, 1-living rooms, 2-upstairs, 3-leisure rooms, 4-annex, if that's possible?
Although the pipe length has some significance, it's really the number of watts travelling down each pipe which is important. This determines the size of pipe required. Read Small Bore heating Systems and Copper Tubes in Domestic Heating Systems.the length of pipework will be fairly long (using 1 or 2 boilers), would an extra pump be needed or would it be fine?
The Atag, Vaillant 37kW system and Remeha Avanta do not supply the total heat requirement. But if all four zones will never need to be heated at the same time, then they are possible contenders.mrbutt said:Atag Q38S
It's probably a good idea to seek the advice of a firm of heating engineers who have experience of large domestic or small commercial installations. Your requirements will be outside the experience of the typical small domestic installer.