Look at the trip times EFLImpudence gave. There's a very distinct difference between trip time for a fault that starts at 0˚ and one that starts at 180˚. It occurred to me last night while trying to get to sleep, that the difference is around 10ms, which is the period of half a cycle. Looks very much like these devices only trip on one half cycle - meaning that if the fault starts in the "wrong" half cycle (ie after 180˚
then there's an extra delay until you get into the right half cycle where the device can operate.
OK, I understand your point now. This is an issue which has been discussed at length in this and/or other forums.
In the case of non-electronic RCDs/RCBOs (if any are still being made – I’m still not sure), it makes no sense that there could/should be any systematic difference in trip times in response to fault currents which starts at the low-to-high zero-crossing point of the cycle (“0°”) as compared with one which starts at the high-to-low zero-crossing point (“180°”). One would therefore not expect to see any systematic difference between “0°” and “180°” trip times.
With ‘electronic’ ones, it has often been observed that trip times in response to fault currents starting at the ‘low-to-high’ crossing point (i.e. “0°”) are generally about 10ms (i.e. as you say, half a cycle at 50Hz) shorter than the trip times for fault currents starting at the high-to-low ("180°") transition point. As you say, the most likely speculative explanation is that the electronics ‘ignore’ the negative half cycle and only respond during the positive half cycle.
If that’s true, why would it be? One can speculate that it’s probably fractionally cheaper to produce electronics which only look at the positive half cycles. If, as they do, these devices achieve trip times well within the required limits even with a fault current starting at the high-to-low transition point, the manufacturers may therefore ‘accept’ that fractionally cheaper approach. If so, it’s a little naughty, since I’m sure that a person through whom current is flowing would welcome as short a shock duration as possible on every occasion (even if their shock starts at a ‘bad point’ in the cycle!), even if the duration is already within acceptable limits.
Is there, I wonder, perhaps a difference in this respect between expensive and ‘budget’ realisations of these devices? EFLI, do you ever see RCBOs which do not show an appreciable difference between 0° and 180° trip times?