In an ideal world I'd have a dedicated circuit for every room, with the kitchen having 3 - one for cooker, one for sockets and one for hard wired appliances.
That would mean a CU with 12 ways for socket circuits!
You say that, but I had a chat with a sparky recently as we were discussing appliance isolation in the kitchen. We both agreed FCUs above worktop are fugly uckers so I 'joked' about having something like a 20a breaker with a 20 amp wall switch for each appliance.
Seen this at TLC. Just over £130 + VAT fully loaded. Not that bad really.
Yeah seen those. My problem with them though is really you need a grid switch/fuse pair to make it sensible (which then looks uglier than FCUs) - no point in having a grid switch accessible and socket inaccessible behind an appliance that the appliance is plug topped into (if the fuse goes you have to pull the appliance out).
I'm trying to find an egraver who will custom engrave my FCUs (suggestions please!) - as Dymo labels look even worse! Sometimes wish I didn't care - life would be so much easier.
The ring is very limited, designed to save copper directly after the second world war in conjunction with the 13A plug it worked well but alterations in building practice and electrical regulations which control how wires have to run and how much wire is allowed have reduced the advantages to such an extent that really it is often better to have radials.
To follow the rules with ring finals in real terms you have to have a 32A MCB but with radials you can have anywhere between 16A and 32A depending on cable used but using 4 mm² may not allow a 32A MCB often reduced to 25A and using 2.5mm² allows a 20A MCB so really needs 6mm² for 32A radial which means in turn no spurs as no room in the terminals.
So really it's 2.5mm² and 20A MCB radial or 2.5mm² and 32A MCB ring. Using 20A RCBO's does mean less trips when there is a fault but using just 2 RCD's really does away with the advantage of the 20A radial. Because the RCBO route is more expensive than the twin RCB route it still works out more expensive to run radials so I would say today radials are in the main better but ring is cheaper.
VD for socket circuits is 5% (I think I mentioned that earlier).
With a Ring Final Circuit (RFC- which your example must be to use 32A MCB with 2.5mm² cable) for VD purposes the best you can really do is calculate the VD to the mid-point of the ring and that point has two runs of 2.5mm in parallel, so it's not 0.018 it's 0.009. The trouble is that the RFC is a kluged design and doesn't really fit neatly with the rest of the regs.
Does a 2-aperture single-gang faceplate with a grid switch and a grid fuse module look uglier than a single-gang faceplate with a switch and a little drawer with a fuse in it?
Still - in the eye of the beholder, of course.