Ring or Radial differences

Joined
18 May 2007
Messages
91
Reaction score
1
Location
Derby
Country
United Kingdom
Acording to BS 7671 I can have as many socket outlets as I want on a 2.5mm ring circuit protected by a 32A breaker (up to 100 sq M)

If I run a radial circuit in 4mm, (with 32A breaker) is there a limit to the no of outlets I can have? (it is no larger than the specified 75 sq M max)

Thanks
 
Sponsored Links
Have as many sockets as you want so long as your 4mm radial is protected by a 32A breaker.

It`s all about load, if you are planning on having many appliances you may want to have another circuit to spread the load.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top