If your bathroom ceiling is more than 2.25m then the lights are outside of the zones. IMO, your installation is safer if you don't mess with it.
There is no requirement to bring older installations up to today's installation standards, even in rental properties.
True, but if there are non-RCD-protected final circuits in the room (even if outside of zones) does that not impose a requirement for supplementary bonding, in terms of both current and older regulations?If your bathroom ceiling is more than 2.25m then the lights are outside of the zones. IMO, your installation is safer if you don't mess with it. There is no requirement to bring older installations up to today's installation standards, even in rental properties.
Plastic pipes obviously don't need bonding. Are there no metal-plumbed radiators (or metal waste pipes, albeit fairly rare these days) in the room?All my water pipes are plastic, so there isn't anywhere to fit supplementary bonding. How does that work?True, but if there are non-RCD-protected final circuits in the room (even if outside of zones) does that not impose a requirement for supplementary bonding, in terms of both current and older regulations?
I would have an electrical installation conditional report done first, then from that you will know what requires sorting out.As I plan to rent the property, I need to the electrics to be certified.
Then you should have an electrical installation certificate for that then, issued by the installer and certification of compliance from building controls.The lighting circuits have no RCD protection and bathroom lights were re-wired in 2011.
If above 2.25mm from floor of bathroom, then they are outside the zones.I have an IP65 rated shower light/fan combo over the bath/shower at 2.27m (if 2.25-3m over bath does that mean zone 2)
That would depend on the way circuit was wired, buried cable will almost always require RCD protections if not mechanically protected.and the rest of lights are outside of the zones. So I believe that to comply with Part P there must be an RCD on the upstairs lighting ring.
The size of the cable and any de-rating factors of the method it which they were installed would require to be calculated, but I doubt a 16A devices on cable sized at 1.00mm would be acceptable, if any de-rating factors are applied.5A is all that's needed on the lighting ring, so would it be permissible to use a 16A RCBO.
No there isn't.There is a grey area within part p with regards to the bathroom zones and notification
in 2011 and outside zones, where not deemed non-notifiable within bathrooms. So should have then been notified!
Not necessarily.My response with regards to BS7671 and RCD protection not notification procedures. But the op does state the circuit was re-wired 2011 and therefore notification would be required regardless.
They were.Also the building regulations were worded differently in 2011
Not so. It was just the same.and outside zones, where not deemed non-notifiable within bathrooms. So should have then been notified!
So if anyone asks, what year should I say it was re-wired?
Eh? What about....Yes but no mention of the definition of the zones of the bathroom as there is now. Which would not have excluded the equipment as outside zones.
?“special location” means a location within the limits of the relevant zones specified for a bath, a shower, a swimming or paddling pool or a hot air sauna in the Wiring Regulations, seventeenth edition, published by the Institution of Electrical Engineers and the British Standards Institution as BS 7671: 2008(2).