Correction factor Ct = ((nv+tp)-(POWER(ca,2)*POWER(cg,2)-POWER(ib,2)/POWER(it,2))/(tp-at))/(nv+tp)
Where nv = Nominal volts (230)
tp = Max permitted operating temp (70)
ca = Rating factor for ambient temperature (1)
cg = Rating factor for grouping (1)
ib = Design current for circuit (26)
it = Tabulated current-carrying capacity of a cable (42)
at = Ambient temperature (30)
For a ring final I can break this down to (300-(1/0.38 )/40)/300 = 0.9999 which is not enough to vary the mA/V/m by enough to really affect the cable length by enough to get 106 meter for a ring final.
11.5/0.0179/26*4 = 98 meters the V/A/m needs to drop to 0.0167 before I can get 106 meters which I was told was the maximum length of cable in a ring final. Even with 25 amp as design current for circuit it still needs the mV/A/m to drop to 17.4 which just seems too much to happen purely due to a correction for temperature.
When I first ran the formula I missed off a bracket Ct = ((nv+tp)-(POWER(ca,2)*POWER(cg,2)-POWER(ib,2)/POWER(it,2))/tp-at)/(nv+tp) and I got that 106 meters which leads me to ask all those years ago (2008) when at the IET lecture had that lecturer made the same mistake? Or is the design current for circuit Ib only 24 amp not 26 amp?
I was told 20 amp centre of ring and rest even so consider it as 12/2 so total = 26 amp.
I tried to make a program to work it out for different values and couldn't get the expected figures so have been trying to get any faults corrected but have reached the stage when I am wondering is there really an error in program or did I get wrong information all those years ago?