You can't prove polarity without an earth
True - but it doesn't have to be an earth from the cable in question!You can't prove polarity without an earth![]()
That's true (but obviously only for TN-C-S) but it seems to represent an extremely deep scraping of the barrel. I suppose that "anything that can happen will happen" (eventually).If polarity is in doubt then a true ground should be used as reference, ... In a worst case error the polarity into the building may be incorrect and the "earthed" CPC is then connected to Live.
That's an interesting, and valid, point. Mind you, if the cable did not have a CPC/earth, then there would not really be an EFLI, in the usual sense, to measure!It is also VERY useful when carrying out the tests on the wiring before it is put into service. EFLI cannot be determined unless there is an "E"![]()
Of course, if it were a TT installation, the EFLI would be an irrelevance, anyway
Interesting, but I somehow doubt that was unique! Returning to TTC's point, did you attempt to measure an EFLI for that circuit?I had an odd one if a factory where the fluorescent fittings were fixed directly to the steel purlins with nuts and bolts. The fitting were fed in two core flex from conduit boxes with TRS glands in. The steel conduit also nut and bolted to the steel work. All ripped out now to make way for a cold store.
I don't imagine that he was, but if he came across it in the course of his work, it may well have been appropriate/necessary for him to undertake tests on the circuit!I have a feeling that he was not resposible for the installation of that!
However, your point raises an interesting question, to which I don't know the answer - how do DNO workers check/confirm the polarity of incoming TN-C-S supplies? I've never seen them stick in an earth rod for that purpose, but maybe they sometimes do. If there are any bonded extraneous-c-p's, they could use them as their reference but what if there are none - do they then rely on testers which utilise capacitive coupling to earth, or what?
Thanks for clarifying/confirming - much as per my speculations, then!The only and I stress only approved use for us of a voltage stick (http://www.screwfix.com/p/lap-ms8902h-ac-voltage-detector-pen/88495) is to prove polarity. We can only purchase specially approved ones from EA Technology http://www.eatechnology.com/products-and-services/field-engineering-tools/polarity-test-kitHowever, your point raises an interesting question, to which I don't know the answer - how do DNO workers check/confirm the polarity of incoming TN-C-S supplies? I've never seen them stick in an earth rod for that purpose, but maybe they sometimes do. If there are any bonded extraneous-c-p's, they could use them as their reference but what if there are none - do they then rely on testers which utilise capacitive coupling to earth, or what?
The only other approved way is with an earth rod, length of wire and a suitable 2 terminal test lamp, this of course needs to members of staff as one has to "guard" the earth rod
Interesting. Was that a practice which was approved by your employer (assuming you had one)? For obvious reasons, it sounds a bit iffy to me - volt sticks aren't too bad when one is trying to confirm that an expected voltage is present (since a 'false' answer is unlikley to result in disaster in that situation), but the concept is much more worrying (at least, to me) if one is trying to confirm that voltage is absent.I used to use volt sticks to check metalwork (appliance cases, rads, sinks etc) for live.