Extending ring main methods
6 Dec 2009
Nottingham
I have extended my property with a new porch/utility room. I intend on extending my kitchens ring main and adding 4 new double sockets to the new room. The washer and dryer will be running from the new outlets.
Option 1 below is the desired arrangement, but my question is specifically about option 2 as this method would be preferable for me due to the layout of the existing rooms and sockets. Is option 2 acceptable under current building regs?
I don't understand option 2 so option 1 it is.
If you can access all the ring wiring then replace it with a 4mm² radial.
Option 1 is the only way to go. I am not quite sure what Option 2 is as it is nothing I have seen before, but it looks like a very odd radial circuit. Assuming that the line shown is one of the conductors (L or N)
Option 2 is not an option.
The correct method is Option 1, and this complies with Wiring Regulations.
I can see why Option 2 might be easier (just adding some figure of 8's to the existing) but you obviously will need the same access to create both options. Option 1 only requires a couple of cables to be joined, and these could be inside the existing socket boxes.
I preferred option 2 because this is how I have installed it (just not connected up yet). I have seen this layout elsewhere in my house, which was professionally rewired just after the part-p scheme came out. It was only when I stepped back and thought about it that it seemed wrong.
I suppose option 2 its equivalent to a 5mm² radial spur off the ring main.
I suppose option 2 its equivalent to a 4mm radial spur off the ring main.
It actually looks to be effectively a 5mm² radial circuit, since it looks as if every socket is supplied by two 2.5mm² (I presume) cables in parallel. Bizarre though it looks when drawn as it has been, it therefore probably would be reg-compliant,wouldn't it?
To be clear, and dependent upon exactly how the connections are effected, isn't it probably electrically equivalent to:
I suppose it would - but some people think four conductors (six with a spur?) in a socket terminal are not allowed (or poor practice).
Would you advocate a 50A MCB?
It's just pointless.
[net]158945/86266_46503735.jpg[/net]
[net]
Yes, your drawing illustrates option 2 more clearly.[/net]
There is no spur proposed but, yes, that is the one possible catch. 4 x 2.5mm² conductors exceeds what is said in MIs for most/all sockets (they usually say 3 x 2.5mm² 'capacity'), but we know that is a bit odd, given that the MIs usually also say that there is 'capacity' for 2 x 6mm².
I'm not sure that I would 'advocate' it but if someone proposed it, and if cable was all 'clipped direct' (and not grouped), I would probably find it hard to argue against it! That's assuming that the two parallel cable paths were of identical length - if not, it would get much more complicated and might not support a 50A MCB. In reality, one assumes thatthe OP would be more than happy with a 32A one!
Indeed. However, we seem to be being told that the OP has already 'done it', so the question is whether it needs to be 'undone'.
4 cables in each socket is going to be very crowded.
And pointless too as you are making the job harder for no reason.
I will be re-doing it properly. Its on a new build and we haven't boarded it out yet so re-routing the conductors wont be to arduous.
Really?
Are you sure?
What did you say, or by default agree, would be the way that compliance with Part P would be achieved?
Can someone just clarify for me please, we are just extending a ring circuit to add two double sockets, yes?
Thanks,
DS