More chance of mechanical damage for the circuits within reach. As I said, it's a guess.
Fair enough - but as IU asked, in what sense is the fixed wiring of a non-lighting circuit (usually) more "within reach" than is the fixed wiring of a lighting circuit?More chance of mechanical damage for the circuits within reach. As I said, it's a guess.
Well in that case so is everything, and I could use 1mm² for any circuit I choose and say "yes, it may very well be supplying smoke detectors, a couple of fans, a shaver socket and a TV, but they are all out of scope, and therefore irrelevant, and therefore it is a lighting circuit."Because your fan, with a plug on, is outside the scope of the standard and is irrelevant to the purpose of the circuit as designed.
But what IS a "power circuit"? How can the designer consider whether his circuit is, or is not, something undefined?FWIW I think that it means "A circuit that the designer considered to be a lighting circuit" and "A circuit that the designer considered to be a power circuit".
From memory BS7671:2008 incorporating Amendment No. 1 (2011).When was 1.0 mm² declared unsuitable for power circuits in BS 7671?
For fixed cables protected by the fabric of the building?More chance of mechanical damage for the circuits within reach. As I said, it's a guess.
It's not really 'wording' but more a change in structure of Table 52.3. In the original BS7671:2008 (red), there was just a single row in the table for "lighting and power circuits', for which the mnimum CSA was 1.0mm² copper (or 16mm² aluminium). In Amd1 (green), this split into two rows, one for 'lighting circuits' and the other for 'power circuits'. the minimum CSA for 'lighting circuits' remained as 1.0mm² copper, bit the one for 'power circuits' was then stated as 1.5mm² copper. The table remains unchanged from that in Amd3 (yellow).Does anyone have the actual wording? My old book is not accessible for inspection.From memory BS7671:2008 incorporating Amendment No. 1 (2011).
Ah, so is that the origin of that confusing Note 5 in the IEC table?In the original BS7671:2008 (red), there was just a single row in the table for "lighting and power circuits', for which the mnimum CSA was 1.0mm² copper
Well, it could, if they forget to remove one note when they inserted an updated one - but it would seem pretty improbable that "Note 5" came chronologically before "Note 4"Ah, so is that the origin of that confusing Note 5 in the IEC table?In the original BS7671:2008 (red), there was just a single row in the table for "lighting and power circuits', for which the mnimum CSA was 1.0mm² copper
Unless it also contained a definition of "power circuit" it is simply impossible for 1.0 mm² to be declared unsuitable for them, for without a definition they simply do not exist.From memory BS7671:2008 incorporating Amendment No. 1 (2011).When was 1.0 mm² declared unsuitable for power circuits in BS 7671?
So it was nonsense then.In the original BS7671:2008 (red), there was just a single row in the table for "lighting and power circuits', for which the mnimum CSA was 1.0mm² copper (or 16mm² aluminium)
Well, a lot less nonsense than it became after the "split", since when the two were lumped together, one did not need definitions to distinguish between a 'lighting circuit' (which supplied power to lights) and a 'power circuit'. At that time, I think most people would have happily taken "lighting and power circuits" to refer to all circuits designed to supply significant power to loads (i.e. excluding only control/signalling circuits etc.).So it was nonsense then. With no definition for it, the table might as well have said "lighting and fnarglebargle circuits"In the original BS7671:2008 (red), there was just a single row in the table for "lighting and power circuits'...
It's certainly odd, but at least it seems to tie in - Somehow! How they got that odd wording in Note 5 and what it's actually supposed to mean is still a mystery though.Well, it could, if they forget to remove one note when they inserted an updated one - but it would seem pretty improbable that "Note 5" came chronologically before "Note 4"Ah, so is that the origin of that confusing Note 5 in the IEC table?![]()