- Joined
- 18 Mar 2008
- Messages
- 1,491
- Reaction score
- 1,090
- Country
The make of your clock and or room thermostat. D.009 figure when the boiler is running for heating.
OP, the differential measured by the d40/d41 is far too small.
It should ideally be 15-20 C.
When you feel the flow and return pipes into each rad, can you feel a slight difference in temperature on each one?
The internal by pass is factory set and would not normally be adjusted by an installer. In any case it would interfere with boiler functioning but the differential on the rads would not be too low like yours, in fact would be likely to be too high. So seems unlikely to be any problem in your case.
Ripper I have a theory that is bugging the life out of me so could you run one simple test for me ? (not trying to step on anybodys toes here) so let the central heating go cold then run a tap for 5 minutes and see if any of the 22mm pipes under the boiler start to heat up.
I reckon your diverter valve is passing, so you got the flow running straight across the plate heat exchanger into the return, that's why its modulating down .