Interesting question.Ok. Lost supply neutrals are not a hazard, then. Why the proposed requirement for earth rod, I wonder?
For a start, do you disagree with my suggestion that there should be no shock hazard within a building whose electrical installation is fully compliant in terms of bonding and earthing (and whose walls are dry
As for possible answers to your question:
1... Maybe they are considering the possibility that some premises have bonding and/or earthing which is not fully satisfactory?
2... As bernard often tells us, if extraneous-c-ps have a very low impedance path to earth, very high currents could flow in the main bonding conductors, leading to a potential fire risk. Furthermore, if that conductor 'melts', main bonding is lost and there is then a risk of shocks.
3... The LFB suggested (or demanded) it!
4... It's not meant to make sense
I think you're being over sensitive. I wasn't being critical but, rather, was pointing out (for Dobby and others) that the situation could be a lot worse than what you depicted. If (as you illustrated) the break was in the neutral supplying only one property/installation then, for a start, one could completely eliminate all risks by opening the main switch in that property. Perhaps more important is the fact that, in relation to (2) above, in that 'single installation' scenario, it's very unlikely (even with exceptionally low impedance path from extraneous-c-ps to earth) that the loads in one property would result in currents which would melt a 10mm² bonding conductor. In contrast, if a neutral break leaves multiple properties with their neutrals connected together, but not connected to the DNO neutral, then those currents could theoretically get very highFor goodness' sake. It's just a simple diagram to explain to Dobby.