I am in the process of buying a new Induction Hob for my kitchen (replacing an electric ceramic hob) but before I finalise my decision on which hob to buy, I want to fully understand the type of change that will be required to the wiring of my house and therefore the likely cost from my electrician. I would therefore very much appreciate some help calculating the diversity of my oven and potential new hob, to determine whether I will need an additional 6mm radial circuit or not.
The situation is as follows:
- Current wire is a 6mm Twin and Earth connected to a 32amp RCBO. There is no insulation between the fuse box and kitchen.
- Oven is a single oven rated at 3.48kw
- Preferred hob is 7.4kw
Total Load without diversity = 10.9kw (10900w/240v = 45.4 amp)
So I have read that the diversity factor for cooking appliances is: 100% of total demand up to 10A, + 30% of the remainder. I guess this is per appliance so:
Oven = 3480w/240v = 14.5 amp
Oven With Diversity = 30% x (14.5amp - 10amp) = 1.35amp
Hob = 7400w/240v = 30.83 amp
Hob With Diversity = 30% x (30.83amp - 10amp) = 6.25amp
Total Load with Diversity = 10amp + 1.35 amp + 10amp + 6.25amp = 27.6 amp
This would mean theoretically so long as I don't use the Ovens Pyro mode at the same time as all 4 hobs on 'super quick boil the water' mode simultaneously, a single 6mm with a 32amp RCBO should cover my requirements.
That said, ideally 2 x 6mm radials would be preferred and prevent the unlikely situation where the draw is greater than 32 amp for more than 10 seconds or so, but my understanding is that this is more usual in an industrial kitchen, where loads are more constant, mine is not. Even on xmas day, the reality is that the oven is maintaining heat at 180 so working only intermittently and the hob wont be on max for the same reason.
Does my logic work, is there anything else that my electrician is likely to raise as a reason for installing a further 6mm radial?
Next step will be to call him and check he agrees with the logic and so is happy to conduct the work on this basis!