oooohhhh matron
They are a bit hit and miss by nature and can easily be fooled by induced voltages from adjacent cables. However as long as you understand and accept the limitations, and don't attempt to use one to prove a circuit is dead, they have their uses. I would say it's worth spending a couple of extra quid for a decent one though.
How does one reliably 'prove' a circuit is dead then when you do not have confirmed access to the conductors (i.e. cutting into a cable run in a roof-space)?
Granted, but that does not 'prove' a circuit is dead. Some cowboy might have wired something through from another building/supply. I'd still use my tester before cutting.If in any doubt then you switch of the main incoming supply at the meter / consumer unit.
Indeed so. As you say, there is a very slight chance that something may be dead even though you think that you have de-energised the entire installation. However, I think the problem you mentioned is only going to arise very rarely. You wrote .....Granted, but that does not 'prove' a circuit is dead. Some cowboy might have wired something through from another building/supply. I'd still use my tester before cutting.
In practice, "cutting into a cable" is a pretty rare event. Electrical work will nearly always involve the ends of conductors, where they are terminated, so one will usually have access to those terminations (and hence can use a 'contact' 2-point testing device) before one actually touches any conductor.How does one reliably 'prove' a circuit is dead then when you do not have confirmed access to the conductors (i.e. cutting into a cable run in a roof-space)?
And face/eye protection(i.e. by using insulated tools and gloves)
Indeed so. As you say, there is a very slight chance that something may be dead even though you think that you have de-energised the entire installation. However, I think the problem you mentioned is only going to arise very rarely. You wrote ..... In practice, "cutting into a cable" is a pretty rare event. Electrical work will nearly always involve the ends of conductors, where they are terminated, so one will usually have access to those terminations (and hence can use a 'contact' 2-point testing device) before one actually touches any conductor.
On the (I would say very) rare occasions on which one is going to "cut into" a cable, then I agree that one has little choice but to do what one thinks has de-energised the entire installation and then probably supplement that with some sort of non-contact tester. However, even then, one should really avoid any contact with conductors (i.e. by using insulated tools and gloves) until the cable is cut and the conductors thus available for proper testing.
Fair enough, but I still think it's a fairly unusual thing to be done.Yes, well I've still managed to need to do that twice in the last year, once when adding an additional socket onto a ring by splicing in the ceiling void and running a loop down the wall.
Yep, anything is possible. The only 'foolproof' approach is to do everything as if one were 'working live', even if one believes that everything is 'switched off' and all 'tests for dead' have given satisfactory results - but that's not really practical, so one has to 'do all one can do to confirm safety', apply common sense, and accept the fact that almost nothing in this world is 100% devoid of any conceivable risks. Let's face it, deaths have been know to result from getting out of bed or putting one's socks on!Even if you did a contact test and read zero voltage differential between two conductors, that might be (however unlikely) because the supply had a transient power cut when you took the test reading and it may become live again 2 seconds later.
There is only one safe method, spike the cable first, using of course a proper spike device not just some Heath Robinson unit.How does one reliably 'prove' a circuit is dead then when you do not have confirmed access to the conductors (i.e. cutting into a cable run in a roof-space)?
TBH he's far more likely to come to harm falling through the ceiling or off the ladder than he is cutting into a cable which belongs to next-door's installation.How does one reliably 'prove' a circuit is dead then when you do not have confirmed access to the conductors (i.e. cutting into a cable run in a roof-space)?
However as noted, you should be wary of all testers.