I did actually phone the DNO, (with little hope) to see if they had any records, but of course they said they don't have such information
Exactly. As I wrote ...So you are suggesting that if the replacement cable happened, the DNO would leave the earth floating? I would have thought they would connect it to the Neutral. Anything else would be scandadous.
The DNO could not leave a situation in which the sheath had become, or been made, discontinuous without making sure that all installations previously relying on that sheath as a TN-S earth were changed to deriving their earth from the neutral.
Apart from the fact that 'it would be nice to know', is there a reason wny you need to know whether it is TN-S or TN-C-S - given that it is clearly an 'adequate' earth?Ze of 0.09...
I'm not being awkward, but I am also having difficulties in understanding why others do not seem to understand my difficulties.@JohnW2. I am having difficulties understanding what you are not understanding.
Work in the street can result in the sheath ceasing to be an effective earth, such that only usable two conductors (L and N) enter the premises, but whether it becomes a "TN-C-S connection" depends upon how it is used. The "S" of TN-C-S means "separated", so if the earth never 'separates' (from the 'C'), it can't really be TN-C-S.Eric said that a TN-S connection could become a TN-C-S connection because of work in the street.
Could you perhaps clarify what you mean by "with the necessary connection of sheath to neutral"? Thanks.Replacement of cable in the street, with the necessary connection of sheath to neutral, can have this effect.
Thanks.Surely John is technically correct in that if the earthing conductor arrives in the premises separately then it is, strictly speaking, TN-S.
I'm not sure I fully understand that "advice". If one "treats a TN-S supply as PME", one would presumably feel that it was OK to connect the installation's earthing conductor to the incoming neutral - despite the fact that if were an 'intact and unmodified' TN-S supply, it would probably not have been PMEd.However, it has long been advised that apparent TN-S supplies should be teated as 'PME' because of the likelihood of the above mentioned (poor and money-saving) repairs in the supply cables by the DNOs.
It looks like TN however only the DNO can say if TN-S or TN-C-S as only they know is some where along the supply root is the earth and neutral have been combined or not.
A big clue as it if TN or TT is the ELI, although a TT supply can have a very low ELI in domestic unlikely to be under the 0.35Ω considered as limit for a TN-C-S or 0.8Ω considered limit for TN-S however with a three phase supply to commercial that does not really work. In one job I spent 6 months knocking in earth rods, non over 8Ω and main earth pit under 1Ω and the incoming earth connected through a large resistor to limit earth current.
So only real way to know is ask the DNO.
As I've said, TN-C-S means that a Combined N and E subsequently splits into Separate N and E. If one does not have any sheath (as with my overhead supply) or does not have an ineffective sheath - i.e only two usable conductors enter the premises - then whether or not it is TN-C-S depends on how we use it. If one 'taps off' the neutral to derive one installation's earth, then (and only then) it becomes TN-C-S.TN-C-S means at some point the earth and neutral shared the same conductor, TN-S means at no point have they shared same conductor, ...
I would call that an understatement - TN-C-S and PME refer to two totally different things - the important thing being that one is not allowed to use a 2-conductor supply as TN-C-S unless it has been PMEd.TN-C-S is not quite the same as PME as some times there are not multiple earth rods ....
In practical terms, that's probably the case. However, even if they don't have records (which I can believe), anyone who opened up the cutout could determine whether the supply is being used as TN-C-S (and that's what matters). As above (and as per my house, as an example), the fact that it could be used as TN-C-S is irrelevant if it is not being used as such (just as in my TT installation).Enquiry as already done is correct method, and if the DNO can't tell you, then nothing more that can be done..
It would, indeed, be an amazing co-incidence if PEFC and PSCC were identical with TN-S. However, I wonder if they really were both exactly 2,500A - it sounds as if that could be a matter of meter precision (or an 'upper limit' of the meter).If the earth loops/fault currents are identical L-N and L-E it suggests PME
Thanks.