so definitly create a new circuit for the outside lights
Where would the isolator go? ThanksYes and include a double pole isolator ( disconnecting both both Live and Neutral ) to ensure a damp or damaged lamp cannot trip the RCD
Brilliant thanks. Makes perfect sense.If you are creating a new circuit from the consumer unit and adding a new MCB for the outside lights then I would put the isolator close to the consumer unit
Sort-of - if you regard "take account of hazards that may arise from the failure of a single circuit such as a lighting circuit" as being a 'recommendation' to do as you say. As you are aware, there is quite a spectrum of individual interpretations of the regulation to which you refer.One lighting circuit for each floor of your house is now recommended
As I said, that's very common - it's certainly true of my house.Yes I have emergency lights to light the stairs, but that is about it. Kitchen has under counter lights, and cooker hood lights independent and near every other room has a table or standard lamp ...
It does - otherwise the under counter lights, cooker hood lights, table/bstandard/bedside lights (and even TVs) are of no use if the lighting circuit fails.It does make some sense not to have lights and sockets in the same room on the same RCD,...
Exactly, that's the point I keep making - that any sort of emergency lighting, whether 'proper' or those cheap 'emergency torches' is the best way of removing potential hazards due to being plunged into darkness, since they will work in response to a power cut (far more common for me than RCD trips) as well as RCD/MCB trips - something that any number of multiple lighting circuits or RCBOs cannot achieve.I would say these .... plug in torches are a better option as they also work with general power cut, and far cheaper than fitting new circuits.
When I moved in a year ago I found there was an error in one switch where wrong neutral was used, only one wire in wrong hole, but potential dangerous for anyone working on the system, as to if this house originally had lights split I don't know, but seen it so many times when lights split where a wrong neutral has resulted.
I could hardly believe it when an electrician who should have known better suggested putting both lighting MCB's on the same RCD so the borrowed neutral would not trip the lights, combining them again so on same overload device yes, but he did not even seem to realise what he was doing was wrong. Some times people do worry me when they are clearly lacking education. But if so called electricians can get it wrong, clearly not a DIY job.
Combining two circuits no problem, i.e. both from same MCB, but putting both MCB's to be powered from same RCD is not, it may work, but not allowed. I have seen it more than once, where the cure to RCD tripping with a combination of two way switches has been cured by putting both MCB's power from same RCD. The other one is where down lights fitted and the load is too high, swapping the MCB from 6 amp to 10 or 16 amp when the ceiling rose is used as a junction box and is rated at 5 or 6 amp.Combining the two circuits is a valid solution to a shared neutral if separation is not feasible or are you referring to the fact they should have troubleshooted the wiring?