@windbagUK , I accept fully your assertion that the replacement 2-port valve has made your E911 alarm go away, but you seem reluctant to accept that any sort of stress testing of the refurbished system would be beneficial i.e. suppose the Sika switch needs a water velocity of 1 m/s to switch and with the old valve in place the average velocity was indeed 1.0 m/s (varying between 0.9 and 1.1). The new valve may give the system an average velocity of 1.05 m/s, varying between 0.95 and 1.15 m/s; a small increase, but within a 'normal' range for this type of valve.
The control strategy, of which neither of us has full details, could monitor the Sika switch every 5 seconds. On each iteration of the 'flow proving' program the system may be programmed not to alarm (E911) unless, say, 3 consecutive underflow conditions are registered. With flow velocity varying between 0.9 (too low) and 1.1 (good) there will be more periods when 2 consecutive 'too low' signals are registered than with the new valve, thus the possibility of an E911 alarm being generated by 3 consecutive low signals will be significantly reduced with the new valve.
I am not suggesting that you remove and replace several zone valves in order to prove a point. I am suggesting that you have a curious mind and you wish to fully understand the reasons why the replacement of one component with an almost identical component would make a problem go away, and I am suggesting ways in which you can seek to reproduce the error message by altering one factor at a time. Once that factor has been established (such as deteriorating pump output) then action can be taken to increase reliability of the system, and using the example of deteriorating pump output, increase the flow velocity to between 1.0 and 1.2 m/s, such as to eliminate completely the possibility of 3 consecutive 'low flow' conditions. Conversely, and easier/cheaper to implement, is to restrict the flow slightly to significantly increase the possibility of the alarm triggering criteria being met. I hope this has made my point clear.
The facts and the variables are clear though.
1. The zone valve makes no signal to the control system - you have stated that the end-switch wires are not connected.
2. The only signal the controls receive is from a simple flow switch - the two conditions are GOOD FLOW and LOW FLOW.
3. The control strategy, and in particular that for the E911 alarm, is not known to us, though we can reasonably assume it is set in software - therefore it may have 'anti-bounce' and 'anti-spurious triggering' algorithms built into it; thus the impression given to the simple observer is that the alarm triggering time is considerably longer than the 10 seconds or so that the valve takes to open fully.