OK thanks, I was just a bit concerned after watching this video say it needed to be on a 20AIf you have an additional 32A radial to the kitchen, not required for a cooker, you could run quite a lot of kitchen sockets off it.
Cheers mate thanks your helpI can't be bothered to watch 10 minutes, but it probably means "if the cable is only 2.5mm"
Thanks for your reply, I currently have 3 separate cables out of the junction box going to a double socket each with a 3amp fused spur from one of them for a cooker hood is this OK?What you have sounds fine, however you have to be careful if you want to extend it.
What you have is essntially a 32A 6mm² radial with a couple of 2.5mm² spurs. It's a slightly unusual case because there are no sockets on the main radial, only on the spurs but that doesn't fundamentally change the safety arguments.
The 6mm² cable is protected against overloads and short circuits by the 32A breaker. The 2.5mm² cable is protected against short circuits by the 32A breaker, but for overload protection it has to rely on the fuses in the plugs.
Since the only overload protection for a 2.5mm² spur from a 32 amp circuit is the plug fuses, there is guidance for what should be supplied from such a spur. Specifically the guidance says it should only supply one accessory either a single socket, a double socket or a fused connection unit.
So if you want to add more sockets, you can't just extend the existing 2.5mm² spurs. You would need to either extend from the 6mm² cable or possibly change the 2.5mm² cables into a ring (though this is non-standard, so some electrians may not like it).