Do that anyhow but I think that MPV is knackered.Ahh I now realised you asked me from to do it from B to A not A to B. I can do that and record the pump readings as well.
When you are controlling the room temperatures by TRVs you should have a ABV, (automatic bypass valve) installed that will start opening when the TRVs throttle right down, Have you got any roomstat installed anywhere? That pump setting CCIII which is over 6M should not be required, as a interm measure I would suggest changing to CCII at 3.0M, it can allways be changed to CP2 at 4.5M, when/if required,I've got TRV valves on all rads. When they are all switched off (set to 0) then the pump shows 32W in the A position.
Honeywell used to have a great name, not so much now I think, installer friends of mine now use EPH but you won't go too far wrong replacing like with like.I've got the Honeywell V4073A1039. Would I have to go and get the same one or can I get away with a replacement?
Was just thinking 7 pages for a seemingly easy fault. I suppose if people keep answering and so does the OP, it may well reach in excess of that!What's the probability this thresd will get to 10 pages?
Andy
No room stat - just TRVs.When you are controlling the room temperatures by TRVs you should have a ABV, (automatic bypass valve) installed that will start opening when the TRVs throttle right down, Have you got any roomstat installed anywhere? That pump setting CCIII which is over 6M should not be required, as a interm measure I would suggest changing to CCII at 3.0M, it can allways be changed to CP2 at 4.5M, when/if required,
The 45watt on HW only shows anyhow that the cylinder coil is not blocked.
If you don't want to install a ABV, you could leave one towel rad or a small rad with the TRV set to 5 (full open) and throttle the lockshield valve to ~ 1 turn open, this will act as a permanent By pass
If I had read your very post properly where you said in very second paragraph that "when i crank up the termostats on the radiators and boiler kicks in I can feel the pipe is hot on both side of the A and B piping" I should have realized that you were referring to TRVs and might then have copped on to the fact that there is no roomstat installed once the pump power was changing, did you tell the heating engineers that there was no room stat(s) installed?, otherwise they may not have asked?, maybe that's a bit surprising in itself.
Its also surprising that the system was installed without at least one roomstat as its very wasteful of energy not to mention constant boiler cycling of the boiler although your boiler Dry Fire protection acted as a very very crude "conrol" with all TRVs closed but of course this then led to conclusions that it was probably a boiler problem.
You should consider getting a roomstat installed, I run my CH in that manner, I have 10 rads, 8, TRVd, two, non TRVd, in a combined dining/sitting room where the digital roonstat is installed so have a very reasonable system as I get pinpoint control of the rooms where we spend most of the day and quite acceptable control of the others. mine is a S plan.
At the end of the day though, you should still be able to run that system with HW only selected but maybe not out of the woods yet, but hopefully the new MPV will cure that.
Hi @Johntheo5, Thanks for your comment.If I had read your very post properly where you said in very second paragraph that "when i crank up the termostats on the radiators and boiler kicks in I can feel the pipe is hot on both side of the A and B piping" I should have realized that you were referring to TRVs and might then have copped on to the fact that there is no roomstat installed once the pump power was changing, did you tell the heating engineers that there was no room stat(s) installed?, otherwise they may not have asked?, maybe that's a bit surprising in itself.
Consider going to an S plan if looking at replacing the MID.I've got the Honeywell V4073A1039. Would I have to go and get the same one or can I get away with a replacement?
I did that test and yes the roomstat turns off the boiler if TRVs set to 5 and I turn the room stat down to 10C. I then turned it up to 22C again and the boiler switched on. After that I had to turn the TRV down to 0 from 5 and again to 5 and observed the boiler firing again. I checked the CH pump after the test and it was showing 19W (I listened to your advise and change it to CCII which seems to be working fine for now).It most certainly could and should. Open up (to 5) a few rad TRVs, turn that roomstat down to 10C, boost or programme CH only ON, check that pump/boiler not on, turn up the roomstat until it cliks on, check pump/boiler running.