How do you wire Nest to Vaillant Combi Boiler?
17 Dec 2018
Nest is not firing up boiler and I need to know whether i have done something wrong
So far here is what i've done the following wiring work
- Using 4 core cable, i've wired two cores to the L and N on both the heatlink and boiler
- The third core is connected to terminal 3 on the heatlink and the other end is connect to RT on the Vaillant boiler
- Fourth core is placed in earth terminal on both the heatlink and boiler
- Used a small piece of brown cable, connecting (jumping) both the Live in the heatlink with terminal 2 in the heatlink
Connected T1 and T2 from heatlink to V3 Thermostat
Anyone know why the central heating wont fire up?
Nest I know, Vaillant I don't. So I am assuming Nest Gen 3 not Nest e? With Nest Gen 3 it has two methods to control boiler, one is volt free contacts, the other is OpenTherm, so to start with which method are you using?
The advantage of volt free is does not matter if boiler uses 230 volt (low voltage) or 24 volt (extra low voltage) it will still work. And since you have access to the com terminal it can work even with a C Plan.
The centre button on the heat link will work even if the thermostat is not connected, so start by pressing centre button, that is what my maintenance guy does to run it when servicing it.
This 1723980298776.png may help others, full guide here. but I have no idea what RT is? I have found one manual which says
Do not connect any mains voltage to the eBUS (+/-) and RT 24 V terminals.
so it seems likely
Was the wrong thing to do, and you need 5 core cable or more likely two cables. Should not run low and extra low voltage together. But boiler type would help.
What is your boiler model?
Assuming yours follows the standard Vaillant wiring methodology, the 230V RT terminal is the correct one to use.
Have you turned the boiler heating controls to continuously on, or is there an existing wireless receiver built into the front of the boiler?
Can you share a couple of pics?
Obviously a gen 3, by terminals the OP has listed.
A good call, but Nest heatlinks have a reputation for failing relays, pressing the button may not give a definitive answer.
Vaillant also use the RT symbol on the 230V return...
I've attached images of the wiring so far
The boiler is a Vaillant ecotec pro 28
This is a Brand new Version 3 Nest Thermostat
Does anyone know why it's not firing up the boiler?
Yes, I have.
Looks correct to me.
If you connect the grey wire in terminal 3 directly to the brown in terminal 2 (after safely isolating power, etc.), does the boiler fire?
Jus to so that I am clear, do you want me to do the following?
- Leave the existing brown cable in terminal 2
- Remove the grey cable in terminal 3
- Add the grey cable from terminal 3 to the brown cable in terminal 2
Yes,
That is what the relay in the heat link does anyway - it simply connects those two terminals together, when there is a call for heat.