Gas smell from boiler after switching off CH
9 Aug 2019
Vaillant ecotec pro 28
Moved into a new property, yesterday we had the central heating on for a while, upon switching off the central heating within a few minutes we could smell gas.
When using the hot water it's perfectly fine.
Heating engineer has been out, serviced the boiler and replaced the flue and turret seals as they were slightly perished.
Gave the boiler a good sniff around and I think it's coming from the flue
Any ideas what would cause this?
Could be the flue and could be products of combustion you're smelling. As above, get it sorted asap and I wouldn't use the boiler until checked
Gas valve passing, needs checked. You would not smell it, when it was burning, boiler in use, but a drop test should show it up.
It layman's terms what does that mean that the gas valve needs replacing or can it be repaired by replacing seals or something?
With no heat demand, your gas valve should close up completely, if it doesn't, then it is permitting gas to still flow, filling your boiler with gas, plus the gas you can smell. If you have a Smart meter, with boiler off, and no gas appliances on, your meter will continue to record some gas use, when it shouldn't.
It usually means a new gas valve, but certainly not something you are allowed to do. You should not even be removing the cover, from the boiler, unless you are GS.
Apologies if this is a stupid question, why would the smell of gas only be present when the central heating is switched off but not be present when using HW or after the hot tap has been closed?
This is why it could be fumes/products of combustion. When using hot water, the fan is ramped up on maximum speed, whereas when using heating it's slower. I attend carbon monoxide alarm activations and have found this to be the case when running the boiler on a lower output. A recent intergas boiler had a similar problem - high fire was fine, low fire set the alarm off.
Imo, if it was the gas valve letting by, it should be evident on either. Again, wouldn't use the boiler until it's checked and sorted. Get your last engineer back.
Your description reads, as if you smell gas, at times when the boiler is not lit, or under low load. That, suggests that under load, the gas is being burnt/consumed by the boiler. Whereas when off, or low load, the leaking gas is not being consumed.
The smell of gas only appears after switching off the central heating
The smell of gas is present for a few minutes, max I'd say 5 minutes if that
When the central heating or hot water is in use there is no smell of gas
5th time .....Gas valve passing - Get a GS engineer to it, as a matter of urgency.
Engineer popped over today, did some checks and confirmed the gas valve was faulty.
He also noticed the pressure gauge increasing above 3 bar despite lowering the pressure from one of the rads whilst the radiators were on
Upon further investigation, the expansion vessel was totally flat, pumped the EV to just over 1 bar and replaced the Schrader valve.
It's been a few hours since he left and happy to confirm the pressure gauge is now stable, no longer increasing whilst the radiators are on however I've noticed the copper pipe outside which I believe is connected to the PRV has a very slight drip, is this normal? If not what would be causing the drip from the outside PRV pipe?
I'm thinking could the engineer have perhaps caused this by pumping the EV too much? Which is now causing the PRV pipe to slightly drip