I missed a crucial "not".
Obviously no reason to have the electrode "not" connected to the MET.
They are - that's literally the definition of functional earth.I thought FE leads were to allow the electronics in the RCBO to work, rather than to carry any current.
There won't be directly connected, but there must be some component(s) between them, and applying 230V AC across the neutral and FE leads will inevitably damage something.I didn't think there was a connection between the FE and N in the rcbo ?
In normal and proper use there isn't any current - until you start connecting the FE lead to an earth electrode that's separate from the rest of the installation as was suggested in the original post, and then the incoming CNE conductor goes open, resulting in 230V or more between the neutral and FE lead, a voltage which will remain there until something goes on fire as even tripping the RCBO won't disconnect that voltage.They wouldn't risk using those tiny wires if there was any chance of current flowing.
Absolutely no difference, electrically - only the words differ, and electrons don't understand words.Are you sure? What is the difference between an additional earth electrode and an extraneous-conductive-part?
Let me get this straight, you are saying safety devices are designed to blow up/cause damage if the incoming neutral is broken?...There won't be directly connected, but there must be some component(s) between them, and applying 230V AC across the neutral and FE leads will inevitably damage something...
Please read the whole thread for context before springing to incorrect assumptions.Let me get this straight, you are saying safety devices are designed to blow up/cause damage if the incoming neutral is broken?
suggested connecting the RCBO FE lead to a separate earth rod and not to the earth terminal.This is page 9 of document on earth fault protection the more I read the more I think the functional earth should go to an earth rod which is not connected to the DNO earth.
I have been following the whole thread but not read the document.Please read the whole thread for context before springing to incorrect assumptions.
This:
If that method of incorrect installation was done, and the CNE incoming cable failed, it could put 230V or more between the RCBO neutral and the FE lead.
In reality this will never happen, as the RCBO FE lead would be connected to the main earth terminal in accordance with the manufacturers instructions. Even with a failed CNE incomer, the FE lead and neutral would still be at the same voltage as they both connect to the same shared N&E terminal.
Which I assumed (correctly or incorrectly) you meant the damage will be internal to the RCBO....
There won't be directly connected, but there must be some component(s) between them, and applying 230V AC across the neutral and FE leads will inevitably damage something...I don't think there is a connection between the FE and N as I have some wylex rcbos with FE, and a time delayed RCD at the origin.
Do any of us actually know what goes on within these things and hence what, when present, these FEs are connected to - or is everyone just guessing?Yes, the RCBO would be damaged if it had 230V between the neutral and FE lead.
Are you sure of this?Yes, the RCBO would be damaged if it had 230V between the neutral and FE lead.
I'm not even considering a combined N & E, only separate from the star point; TN-S (as I believe I have at home) or TT.When connected correctly that is impossible, as the neutral and earth terminal will be at the same potential, even if the incoming supply cable has a break in the combined N&E conductor.
The damage would only occur in the specific circumstances suggested in the opening post of this thread.
I'm sure there are, and if/when I have some time I may look - but I was wondering whether anyone already knew the answer.Plenty of videos on YouTube on the inside of rcbo.
If I understand correctly, only the earliest RCDs used just current from the sense coil directly to operate the trip mechanism. Subsequent ones have seemingly invariably added electronics to the equation (hence might be perceived as needing an FE to ensure there was always voltage to power the electronics) - I imagine, conceptually, to 'amplify' the current from the sense coil.I assumed RCDs were a toroid with 3 windings. I guess the type A must be more advanced.
It seems two methods with electronics, active RCD's fail safe, loose the supply and it auto disconnects, or the FE and passive type.If I understand correctly, only the earliest RCDs used just current from the sense coil directly to operate the trip mechanism. Subsequent ones have seemingly invariably added electronics to the equation (hence might be perceived as needing an FE to ensure there was always voltage to power the electronics) - I imagine, conceptually, to 'amplify' the current from the sense coil.
Indeed, but (a) that 'NVR' functionality does not necessarily require electronics and (b) that introduces an additional complication to the discussion - so it would probably be best to just thing/talk about passive RCDs, as found in CUs.It seems two methods with electronics, active RCD's fail safe, loose the supply and it auto disconnects, or the FE and passive type.
Indeed, but that question is pretty moot - both 'loss of PEn' and 'earth fault' are very rare events, so the probability of the two occurring simultaneously must be pretty close to zero.But question remains, with loss of PEN will they still disconnect if there is an earth fault?