- Joined
- 27 Jan 2008
- Messages
- 28,483
- Reaction score
- 3,459
- Location
- Country
Noted a new Martindale EZ664 and EZ668, they also do CP501, BZ101, CP520, BZ701, EZ165, and EZ365. Some with and some without loop impedance test, and some with and some without RCD test. There are also of course different makes, and some will show line - neutral reversal, and claim "Detect presence of earth" and under and over voltage.
However, earth loop impedance pass level is typically 1.7Ω and under over voltage <195V or >270V and if the neutral to earth voltage is >30V. And the RCD test is for 300 mS, where we would normally look for 40 mS.
I used to have one in a caravan to test line - neutral reversal, was easy on continental caravan sites in the 80s, but when we got the last batch of caravans, we had proper testers, and did not take it abroad, and line - neutral reversal is unlikely in the UK. And one caravan, it was built into the consumer unit, and could be swapped at the consumer unit by pressing one button.
My loop impedance tester will take a lead with 13 amp plug, so does the same as the plug in testers, but actually shows mS, tripping currents, tripping time, and voltage, and leaves it to me to decide if within range.
I have seen the plug in tester in tool kits, but have no idea why carried, but the question is, do the users think if correct lights have lit, all is OK, as I have said many times, a ring final was 1.44Ω, now 1.38Ω, with a B32 MCB, so why pass at 1.7Ω?