Is this main breaker box and subpanel setup correct?
10 Jun 2024
Mauritius
Hello
This is the main breaker box in the house downstairs:
And this is the other breaker on the first floor found right above the main breaker box:
I want to understand what these breakers mean (are these values correct?) and if the setup has been done correctly (i checked some YouTube videos and it seems like the main breaker in this case might be the 63A but it should have been installed on the far-left side?). I counted the breaker total Amps and it comes to 66A but the main breaker is only 63A??
I also want to check if the neutral busbar (if it even exists in this connection box?) has been connected to the ground busbar in the main breaker box. Is it safe for me to unscrew it just to check inside? I can see two Philips screws on each side of the panel.
Thanks in advance for any help.
That is quite normal.
It is considered highly improbable that all the circuits in your house would be drawing maximum current at the same time (or, indeed, ever).
The principle is called "diversity " and there are some rules for calculating it, I don't know what they will be in your country, but your figures look fine.
DO NOT connect the ground to the neutral without consulting local regulations first.
Americans bond ground and neutral in the main breaker panel, but this is a quirk of american practices, not a universal global standard.
These Legrand MCBs have shrouded terminals. Check if the 63 A disconnects all power to the house. If it does you can safely remove the front cover and have a look at the wires.
Not really.
The TN-C-S system requires that the Neutral be bonded to the Earth.
How else can the "Neutral" be a Neutral, unless it is bonded to the Earth?
TN-C-S is used almost universally in North America and Australia.
It is also used in the UK - and many other countries
See https://en.wikipedia.org/wiki/Earthing_system
Not really.
Remind me what the "S" stands for in TN-C-S
In the UK it's up to the supplier to determine if a supply is suitable for TN-C-S. If it is then they will supply an earth terminal which is bonded to their neutral wire. In normal installations neutral and earth are kept entirely seperate on the customer side.
I stand by my position that people should not go adding neutral to earth bonds based on stuff they have read on foreign websites.
Usually if the supply is a TN there’s pretty clear rules if and where the neutral is to be connected to the earth in the customer‘s house and how the PEN is to be divided into neutral and earth. These can vary even within one country.
If it’s a TT supply, there’s no connection between neutral and earth at the house at all. Introducing one is a pretty bad idea.
You need a local electrician to tell you how your earthing arrangements should be.
The Electricity Safety said:
(4) A consumer shall not combine the neutral and protective functions in a single conductor in his consumer’s installation.
In the UK the connection between neutral and earth is not done by the consumer, however when the supply is local it does need doing in the consumers' installation, so with solar panel inverters there is a relay to connect neutral to earth when the DNO supply is lost.
I can't find a ref to TN-C-S in ESQCR, only PME, maybe I have missed it? But the M stands for multiple, and I believe with TN-C-S there does not need to be multiple connections to earth.
It is hard enough to work out what is permitted in the UK, never mind other countries, what we need to realise is BS 7671 is not law, but ESQCR is, and BS 7671 is used by other countries as well as the UK, it does state in some sections where the ESQCR requires something, like the earthing arrangements in caravans and boats.
The US are 100% TN-C-S. Some areas split the PEN at the meter and run neutral and earth to the main distribution board but most run the PEN (referred to as neutral and coloured white) all the way to the main DB, which has a factory link between the neutral and earth bus bars. If used as a sub-board, the installer needs to remove the link. A main earth from an earth rod or earth mesh in the concrete footers or slab (called UFER if I remember correctly) is also connected to the point where the PEN is divided.
Until at least 20 years ago larger circuits (cooker, tumble dryer, 30-50 A 240 V) were even TN-C, i.e. the PEN was run all the way to the appliance and connected to the neutral and earth terminals of the appliance.
The Germans used to run the PEN all the way to each DB well into the 2000s but usually earthed the PEN at the service cutout. That practice was abolished for new installations because it was likely to cause stray currents in pipes and other bonded elements of the building if there were multiple DBs. In practice that often means you have to convince the DNO to fit a new cutout if the old one doesn’t have enough terminals for incoming PEN, outgoing neutral, outgoing earth and bonding conductor to the MET. Proper old ones (cast iron) only have one for each PEN, that’s it. There were plenty of regional differences though, Hamburg required separate neutral and earth from the meter as early as the 1950s while sparks in Berlin happily ran TN-C into each flat until the late 2000s.
Because they use (mostly) TN-C-S
Well, yes but it is TN-C-S because they bond ground and neutral at some point; not the other way round.
So they just bond at a different place than do the UK.
I was getting the impression that they - the US - bond in the CU as well.