I can measure total leakage with ease,
but leakage for each RCBO would require me to remove the cover from the consumer unit, with a test of all 14 would need to do that anyway, but that only happens on the odd time, the testing of socket outlets which are more likely to need RCD protection is more regular.
But to take away the leakage requires a ramp test, and with a ramp test, one is not testing the time to trip. But if doing a ramp test, one does not really need the ½ test, but the schedule of test results should have leakage, ramp mA, and time for 30 mA test to see if anything is degrading, and the standard schedule does not have the option to record these results.
The same applies to line - neutral loop tests, we know it needs to be taken to work out volt drop, but since not recorded one can't see if A always been too high, B some degrading, C the loop impedance tester is likely faulty. If recorded, it would alert one to a change, and one would look at why. But if vital information missing from the form, why bother recording anything, may as well simple write pass or fail? Not talking about why test, talking about why record silly info like the maximum tripping time, we know the maximum permitted is 40 mS, what needs recording is the highest of + or - and now don't need to measure both so just the tripping time.