10mm Cable Capacity.
9 Oct 2007
Tyne and Wear
Hello all, just a quick question.
I am planning to upgrade my shower to a 10.8 kw unit and upgrade my wiring to 10mm twin and earth. (usual run in a standard terraced house).
I'll need to replace my old 30 amp MK mcb with an uprated unit but the only ones I can get from my local retailers are 40 or 50 amps.
My question is, will my cable be up to carrying 50 amps if required? I've had a quick look in my on site guide and it seems close and will depend upon the installation method used. Which method applies to this installation? (usual plaster walls/under floorboards etc)
Any help is gratefully recieved.
Biffco
10mm can carry about 60 amps optimum (depending on the length and route (derating factors) of the cable)
10800watts/230volts=46amps. You need a 50 amp MCB.
It depends how you run the cable, if it is clipped and not in a thermal insulated wall, you can use the 50A. I would recommend that you use the 40A unit, as there are many other parameters that will influence the capacity of the cable. if it is not too late I would consider to get a lower capacity shower or use a different type of cable that can carry more than the T&E.
BTW a job in a bathroom is a notifyable job.
Steve, electric showers sold in the UK are commonly rated at 240V, so the current drawn by 10.8kW would be 45.0A. Doesn't change the advice of course. ;)
Always best to do load calculations assuming 230V Softus, errs on the side of caution.
I disagree - it's best to look on the shower label or in the documentation.
If a shower rated at 240V is then run at 230V, then the current will be less, not more, than the design loading.
This isn't about opinions; it's about accuracy and safety.
I'm not really sure what you're getting at here Softus but I'm sure you'll enlighten me :wink:
If you work out loading for cable size based on 230V rather than 240V you will always end up overspecifying capacity ... Which is safer, is it not?
[email protected] :lol:
If you blithely overspecify the design current for a known constant load then it isn't safer. :roll:
I'm thinking that the 40 amp breaker may suffer from nuisance tripping, so I would prefer to use the 50 amp unit safely if possible.
As for the cable run, which installation method number correctly refers to running in a house? Most state run in conduit in a wall or clipped direct among the usual examples. Could someone point me towards a table whereI can see the cable ratings for myself please?
Thanks, i'll go and dig out my n site guide before I go to bed. I did look earlier and I thin that table states 40-45 amps if we assume method no 4 (if that is the correct method)
I may have to opt for a 40 MCB
4D5A :wink:
You base the MCB size on the design current of the circuit. You base the size of the cable on the MCB size including de-rating factors.