Eighty KW of boilers and £1800 a month for heating only which is nearly £22K![]()
He He He.. Got to be a firm of Solicitors.
I have a pal who has a huge three floor farm house and offices heated with a 40Kw oil boiler and his oil bill is only £450
Hi again,
Previous bills are between £1600 and £1800 for the last 6 months, that is why it has been passed to me. I dont have the actual bills just the readings and invoice costs.
I have been watching the meter and I timed 60 seconds.
Metric meter
Start reading 413349 0/10
End reading 413349 9/10
The boiler details are
Ideal Concord 170 Series 4
Heat output 48.4Kw / 165000BTU
Heat Input 62.1Kw / 211500BTU
Meter is stationary when the boiler is off.
Hello,
Doitall, thanks for working that out for me. I will request the actual bills tomorrow to check.
We are not a firm of solicitors, we are a steel engingeering firm specialising in heat treatment. We do have a cinema but only air source heat pumps, not situated in a field but a grotty part of the north.
The £1800 is for this single boiler per month alone.
What is wrong with Keston? Not that we are replacing it, heat pumps are the way forward in this building.
£1800 is easily lost when your total gas consumption for the month is £80-90K
Now we know the meter is corect, I know that there is a billing issue instead.
Thankyou all for your help, it has been appriciated.
Incidentally, why would anyone condemn a safely working boiler? Surely that weakens the position when a gas appliance is condemned on safety grounds?
Hello,
Hello,
Yes,but generally you have to find as many safety issues that you can in order to cover yerself.
Not difficult on any boiler never mind one as old as yours![]()
Hello,
These boilers are around 79% so not that bad. I would think the problem lies with the system pipework, Isolation or lack of, and an virtually open building. The heat loss must be astronomical.
Hello,
I've seen a lot of them installed with 22MM pipework right off the boiler tappings.
All that happens is they then continually cycle on the thermostat with very little hot water going away from the boiler.
Some of the older ones just had a thermocouple with no overheat stat.