bs3871 zs value ?
27 Jul 2008
Can anyone tell me the zs value for a bs3871, 32 amp, b type mcb ? or where it is in the 17th, cos I cant find it !!
If you take the 48/In divide by 240 times 230 then you get the 46/In given in new 17th Edition so 46 divided by 32 gives 1.4375 ohms Table says 1.44 ohms same applies for example Type 1 so 57.5/In so 1.796875 ohms for 32 amp using excel you can quickly make a table.
Eric
Eric
Blimey, make it hard for yourself why don't you?!!
The Zs values are calculated by Uo/Ia, as can be seen from the equation on page 48 of the 17th Edition.
If you have the old values, they were calculated using 240V , whereas the new ones are calculated using 230V, so simply multiply the old values by 230/240 (multiply them all by 0.96 and you'll be close enough.)
Looking at Easycert, the software I use to create certificates and reports, it has a BS3871 B32 at 1.44ohms.
EDIT - I'm not convinced they have it correct though as I believe a type B is the same as a type 1, a type 1 has instantaneous tripping characteristics of 2.7-4.0 x In.
That would mean 230/(4x32) = 1.79ohms
Guide to circuit breaker standards
thank you both very much for your replies. Do you recommend easy cert ? I currently hand write all my test certificates, however i'd like a more proffesional system. Can I use these with Elecsa ? or do i need an elecsa logo on test sheets i produce ? (im registered with elecsa )
I must admit I thought the type B came in with BSEN60898 devices, the old BS3871 being type 1, 2, 3 or 4.
The 1.44ohms you get from the easy cert is the same as whats in the regs for a BSEN60898 type B device.
Yes, I noticed that.
I also though BS3871 MCB's came as types 1-4 only but the document I posted above says otherwise.
Yes, I would recommend EasyCert. Have a look at Tysofts homepage and download the evaluation to have a feel for the software.
Tysoft EasyCert
We're with the ECA and I don't have a problem adding the ECA logo to all certificates or reports I produce.
Guess what?
I've got a photo of one :lol:
The MCB is designed to magnetically trip at a set multiple of the designed thermal over load current. So putting it in simple format.
Type Multi fig x/In 240V x/In 230V 32A 240V 32A 230V
Type 1 X4 = 60 or 57.5 Max ELI=1.875ohms 1.796875 ohms
Type B X5 = 48 or 46 Max ELI=1.5 ohms 1.4375 ohms
Type 2 X7 = 34.28571 or 32.85714 Max ELI=1.071429 ohms 1.026786 ohms
Type 3-C X10 = 24 or 23 Max ELI=0.75 ohms 0.71875 ohms
Type D X20 = 12or 11.5 Max ELI=0.375 ohms 0.359375 ohms
Is that any better then. Sorry seems it don't like tables or ohm sign! Fancy having an electrical forum that can't accept an ohm sign!
Eric
Yes, I'm with RF here. Type B/C/D breakers were introduced under the old standard BS 3871, alongside Types 1-4.
Although there was not a Type A, as "A" denotes the unit of current measurement.
P111 of GN3 gives max measured values, not max tabulated values.
There is a factor of 1.24 difference. (1.24 given for a 60ºc temp difference between max and measured)