In a larger TT install with submains you still need something to protect the submains and you probablly don't want to use a 30ma because you will want discrimination with other RCDs downstream.The point that ericmark was making is that under the current regs, there is no practical use for them anymore, as you have said, the norm is to install either a dual split or all RCBOs for domestic installations, so there is no need for a 100mA RCD, even on TT supplies.
Doesn't a need for a 4-pole RCD hint that this is probably not a domestic installation?The point that ericmark was making is that under the current regs, there is no practical use for them anymore, as you have said, the norm is to install either a dual split or all RCBOs for domestic installations.
Time delayed is referred to as S type.
100ma has no real use any more for fire you require 300ma (see 532.1) and for sockets over 32A in construction sites 500ma (704.411.3.2.1) and for cables buried in walls under 50mm and for sockets under 20A (some places under 32A) it needs 30ma (415.1.1) so the 100ma trip is no longer stipulated for any use so they are really only old stock.
Although in the commercial field you get many variable RCD's these are only permitted to be used by skilled personnel so are not used in domestic.
Why do you want a 100ma RCD?