17th Ed Part P Question

Joined
27 Sep 2006
Messages
71
Reaction score
0
Location
Dorset
Country
United Kingdom
A customer wants to add a spured socket to an existing ring final. The CU has MCBs with no RCD protection and no spare ways. There's no way they'll go for a CU change just for one socket and I very much doubt that adding a socket with built-in RCD is good enough to conform to Regs.

How would you get around this?
 
Sponsored Links
I very much doubt that adding a socket with built-in RCD is good enough to conform to Regs.
Why?

It's only your addition that has to comply, so an RCD socket would.

And don't forget 522.6.6 - it may be that putting an RCD FCU directly onto the existing circuit and then running to the new socket is the best idea.
 
I understand the rules to be that any circuit I work on has to be compliant with the regs, not just any extension I do to an existing circuit. If I've got this wrong then I'll be a very happy bunny indeed.
 