2.5mm High-Tuff Cable - Circuit Protection

Discussion in 'Electrics UK' started by CAWORK, 22 Oct 2019.

  1. CAWORK

    CAWORK

    Joined:
    12 Jan 2006
    Messages:
    157
    Thanks Received:
    1
    Country:
    United Kingdom
    Good Afternoon,

    I wish to install an outdoor twin socket on the outside wall of my parents stone cottage. I have considered using Hi-Tuff cable (grey in colour if possibly available) as I consider this to be the neatest looking solution.

    My intention is to spur off a nearby indoor socket, which is part of the RF circuit and run the cable through a hole drilled in the bottom corner of the window frame and have cable clipped direct inside and out (inside socket is in store room at back of house so looks are not too important- would be absolutely impossible to drill straight through the wall).

    However my main question is regarding the circuit protection/current rating of the 2.5mm Hi-Tuff cable, since it is of a flexible construction (rather than a solid 2.5mm T&E) is it satisfactory to be protected by a 32 amp protective device?

    I understand a single 2.5mm spur from a RFC is satisfactorily protected (according to a previous issue of 'Switched On' magazine from overload, short circuit and earth fault protection although you need to be a mathematician to understand the calculations explaining why this is so).

    Also where can I buy Hi-Tuff cable from? screwfix and Toolstation fairly near me do not appear to sell it.

    NB
    RFC in house protected by 30mA RCD.

    Many Thanks
     
  2. Sponsored Links
  3. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    34,556
    Thanks Received:
    3,829
    Location:
    Retired to:
    Country:
    Portugal
    Not for overload, it isn't, but for fault protection, yes - if the circuit is not too long.
    The overload protection is by the two 13A fuses in the plugs.
    2.5mm² flexible cable is rated at 25A; twin & earth 27A - so I wouldn't worry about the 1A.

    As above.
    There is a rather complicated equation to determine if the CPC(earth wire) is large enough although this would not apply to flexible cable as the CPC is the same size as the others (unlike twin and earth).
    All you have to worry about is the 25A which is unlikely to occur.

    Hi-tuf is rather difficult to work with - any flex will do - black is better for outside but it's up to you. White might not last as long but still years.

    Good.
     
    • Thanks Thanks x 1
  4. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    34,556
    Thanks Received:
    3,829
    Location:
    Retired to:
    Country:
    Portugal
    You could, of course, use 4mm² flex which is rated at 32A and not have to worry about anything but it is not necessary for one double socket.
     
  5. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,081
    Thanks Received:
    148
    Location:
    Derry, Ireland
    Country:
    Ireland
    Hi-Tuff is always black sheathed. NYM-J is grey but isn't UV tolerant (nor is it BS compliant but is a VDE product).
     
  6. Sponsored Links
  7. davelx

    davelx

    Joined:
    26 Sep 2006
    Messages:
    1,731
    Thanks Received:
    135
    Location:
    London
    Country:
    United Kingdom
  8. aptsys

    aptsys

    Joined:
    16 Sep 2007
    Messages:
    1,796
    Thanks Received:
    135
    Location:
    Cambridgeshire
    Country:
    United Kingdom
    Looks OK to me
     

    Attached Files:

  9. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,081
    Thanks Received:
    148
    Location:
    Derry, Ireland
    Country:
    Ireland
    It's not suitable for external use (unless in conduit etc.)

    Trust me - it's a commonly used cable in the south of Ireland.
     
  10. markyd1

    markyd1

    Joined:
    7 Jul 2019
    Messages:
    84
    Thanks Received:
    7
    Country:
    United Kingdom
    And still no mention of a minor works cert for addition
     
  11. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page