2 metre long rad won't heat up

Joined
14 Oct 2008
Messages
995
Reaction score
13
Location
Surrey
Country
United Kingdom
I've just fitted this in my uncle's house, the rad is a double and has the flow and return pipe on the right hand side (top n bottom), both pipes get hot, the right hand side of the rad gets warm but the left struggles to get tepid, the rad has no air in, both the lockshields are new...........what'dya think?
 
Sponsored Links
Water will take the easiest route. Having both valves on one side gives it no "reason" to flow through across the radiator.

Solution - extend the pipework to have a valve at each end of the rad.
 
Technically it should work, but sludge will build up in the opposite side to the valves.

How long has it been installed.
 
Technically it should work, but sludge will build up in the opposite side to the valves.

How long has it been installed.

Indeed it should, but it sounds like it's just made the majority of the rad a deadleg. The op used the word "just", which implies quite recently. ;)
 
Sponsored Links
It's been fitted for 24hrs, the whole system has been flushed (not powerflushed) about 5 times
 
Try tightening down the lockshield a bit to "hold" the water in there a bit longer.
 
Dextrous..............yeah, tried that but to no avail.

Thanks lads, I'll change it to lockshields at each end
 
As others have said, connecting flow and return to opposite ends is recommended.

Connecting both to the same end might work, providing the flow is connected at the top, and the return at the bottom.

If you have connected the flow at the bottom, the hot water will just whiz straight up the first column and out the return without heating the rest of the rad. That sounds like the problem you have.

Connect the flow at the top, and the lower density of the hot water may be enough to keep it at the top of the rad, spreading further along, but 2 metres is probably too far for that to work effectively.
 
Yeah, the flow is at the top, but the bottom left of the rad hardly gets above cold..............so there's no option!
 
As others have said, connecting flow and return to opposite ends is recommended.

Connecting both to the same end might work, providing the flow is connected at the top, and the return at the bottom.
Why shouldn't it work? TBSE is, after all, the connection method used when the radiators are tested under BS EN 442. The flow has to be at the top.

The OP said:
both pipes get hot
There should be a noticeable temperature between flow and return (compare with other rads). If there isn't, the lockshield valve is not closed enough. If you have not adjusted the LS valve, try it one turn open from fully closed. Closing the valve increases the temp difference and vice versa.

Adding this new rad may have upset the balance of the whole system.
 
D.Halisham ..... This is where your googling of information lets you down in preference to experience of working on systems and actuallyknowing what works and what doesnt.
 
flow to the top should work, depends on water velocity, I would never have done this anyway, it will allways be a pain. :!:
 