if you think about it fellas it's a bit like forgetting the spreader tube on the old twin entry valves
pipes get hot rad don't
pipes get hot rad don't
That's putting the cart before the horse. You achieve the correct temperature differential by getting the flow rate right, which you do by getting the differential pressure correct. But as most installers do not carry the necessary kit to measure the flow rates and differential pressure across the radiator, they just look at the end result, i.e. the temperature differential.Getting the flow rate "correct" is solely a matter of producing the temperature differential appropriate to the BOILER's expectations.
Not strictly correct. It assumes that the flow temperature does not get any lower. A 1000W radiator (at 75/65/20, i.e 10C differential) will produce 1070W at 75/70/20, but only 915W at 70/65/20 (both 5C differential).The lower the differential the more heat output from the rad!
Oh, is it? With the last boiler I installed, there were M.I. specifying a set flow and return temperature, nothing about flowrates through rads, or any of that.That's putting the cart before the horse. ...Getting the flow rate "correct" is solely a matter of producing the temperature differential appropriate to the BOILER's expectations.
I wouldn't expect the MI's to say anything about radiator flow rates as the flow rate will depend on the radiator output.Oh, is it? With the last boiler I installed, there were M.I. specifying a set flow and return temperature, nothing about flow rates through rads, or any of that.That's putting the cart before the horse. ...Getting the flow rate "correct" is solely a matter of producing the temperature differential appropriate to the BOILER's expectations.
What did the M.I. of the last boiler you installed require, any flow rate or flow speed in particular?
OK! and I promise not to say anything about Tour and Anderssen's Balancing Manual or their Computerised Balancing Instrument.Dave, Just don't mention DRV's and control stations.
Water goes out the boiler, through the rads, back into the boiler. If the water going through the boiler is not the same as that going through the rads, where is it going?I wouldn't expect the MI's to say anything about radiator flow rates as the flow rate will depend on the radiator output.Oh, is it? With the last boiler I installed, there were M.I. specifying a set flow and return temperature, nothing about flow rates through rads, or any of that.That's putting the cart before the horse. ...Getting the flow rate "correct" is solely a matter of producing the temperature differential appropriate to the BOILER's expectations.
What did the M.I. of the last boiler you installed require, any flow rate or flow speed in particular?
The flow rate through the boiler is not the same as the flow rate through the radiator...
And then along comes the problem rad and no-one knows what to do, other than the obvious and easy way out which is to repipe it BBOE.
But we are talking about a two-pipe system, so all the water does not go through each radiator. Even on a one pipe system, some of the water is diverted to bypass each rad. If it wasn't, shutting off one rad would shut of all rads.Water goes out the boiler, through the rads, back into the boiler. If the water going through the boiler is not the same as that going through the rads, where is it going?
Please don't misquote me.bengasman said:And if you don't expect the M.I. to mention anything about flowrates, what do you expect them to mention?
What I am talking about is all set out in this diagram. The boiler and rad sizes have been selected to make the maths easier.D_Hailsham said:I wouldn't expect the MI's to say anything about radiator flow rates as the flow rate will depend on the radiator output.