230v room thermostat or 24v ?

Joined
11 Nov 2019
Messages
3
Reaction score
0
Country
United Kingdom
My boiler specifies 24v for the room thermostat. Do I have to use a 24v specific thermostat or can I use a 230v one? I have seen some specs for the stats as having a supply voltage of 24v-230v. Thanks.
 
you need a voltage free contact thermostat most are these days, some are battery powered , some are mains powered, what boiler do you have and what thermostats are you looking at? do not put 240v into a 24v boiler or you will make a very expensive mistake
 
It's quite an old boiler, a Ravenheat. I was looking at a simple wired mechanical one like the Honeywell T6360. I think the T6360B is the 24v rated one.
 
I'll have a look at that, thanks.
 
Last edited:

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top