I have and I doIf you have any experience of this then you will know that a motor designed to operate at 400 volts in delta can be started in star which gives approx 58% voltage across the windings but also means approx 58% of the maximum torque as well.
?????????????If you have a motor designed to run at 695 volts star then unless it is virtually running free it will not start at approx 33% (230v) of it's rated voltage when started in star. The motor will probably stall and the overload will operate if correctly set.
Believe me, I have experienced it !
You are making the same mistake as many and misunderstanding motor rating plates
a motor designed as you say to run at 695 star is equally designed to run at 400v delta
delta = voltage rating of 1 coil
star = 2 delta coils in series (hence higher voltage rating)
so if a 3ph motor is rated for example 230/400 then it would be connected to a 3ph 400v supply in star config or a 3ph 230v supply in delta config
a motor rated 400v/695 would be connected to a 3ph 400v supply in delta, or if it was a biggun, for reasons you have already given
either connected to a variable speed drive or connected star to start and delta to run to enable it to soft start.The motor will probably stall and the overload will operate if correctly set.
many times I have had to strip out motors to take for rewinds because they have been 400/695 rated and connected in star to a VFD