Absolutely no need. Even a 60A supply would be more than ample. In fact you need advance permission from the DNO to exceed 60A/phase with an EVSE.
Pay attentionTable 54.8 is for bonding conductors; not earthing conductors
542.3 Earthing conductors
542.3.1 Every earthing conductor shall comply with Section 543 and, where PME conditions apply, shall
meet the requirements of Regulation 544.1.1 for the cross-sectional area of a main protective bonding conductor. ...
That may be true for the OP but, in the more general case, 60A would not necessarily be 'more than ample', unless one were perhaps prepared to accept very slow EV charging - it all depends upon the 'other loads'.Absolutely no need. Even a 60A supply would be more than ample.
I think that one who used to contribute to this forum got something right about my question in a thread when, indeed, I myself got it wrong, after a while I realised he was correct (Some of you will remember dear old Ban-All-Sheds)Pay attention
I also mentioned 542.3.1, and that says that, when there is PME, Earthing conductors also have to satisfy the requirements for bonding conductors with PME (i.e. comply with Table 54.8)! ...
Yes, many of us rememberI think that one who used to contribute to this forum got something right about my question in a thread when, indeed, I myself got it wrong, after a while I realised he was correct (Some of you will remember dear old Ban-All-Sheds)
If you can afford to pull more than 60A constantly through the night then you should probably just rapid charge your EV rather than fit a chargepoint, and heat your house by burning banknotes in an open fire.That may be true for the OP but, in the more general case, 60A would not necessarily be 'more than ample', unless one were perhaps prepared to accept very slow EV charging - it all depends upon the 'other loads'.
542.3 Earthing conductors
542.3.1 Every earthing conductor shall comply with Section 543 and, where PME conditions apply, shall
meet the requirements of Regulation 544.1.1 for the cross-sectional area of a main protective bonding conductor. ...
What else can it mean, other than 'what it says'?If that means what you state then it must be one of the worst worded regulations.
What would that change (in terms of the point I was making)? It would still surely mean that (with PME) Earthing conductors have to comply with 544.1.1 ('as if' they were bonding conductors), wouldn't it? It's surely not for us (or anyone) to invent a reg which says what we believe it should say (even though it doesn't), is it?Surely it should state instead rather than and.
Why not? It's surely often the case that there is a requirement for something to comply with more than one reg. "Complying with 543" means things like being shown to be adiabatically adequate (or compliant with Table 54.7) - but that is not incompatible with an additional requirement to comply with 544.1.1 ('as if' they were bonding conductors), it it?The conductor cannot do both comply with 543 and then do something else.
I wrote that deliberately since I personally felt that they probably 'got it wrong', since it would seem to me that it is TN-C-S (not PME) that could impact on the required size of bonding (or earthing) conductors.Also above when explaining, you write "even with a 'PME' (TN-C-S) supply" but they are not the same ....
As above, I don't think that whether or not there is 'PME' has any bearing on requirements for bonding/earthing conductors. As you say, when a supply enters a house as TN-S one has to consider the possibility that the earth path involves a PEN conductor - and that could be relevant in terms of requirements for bonding/earthing conductors..... plus these days we have to treat all apparent TNS supplies as PME and, as you know, the 'M' might only be two.
Well, unless you're going to invent your own version of what you believe the regs 'should' have said, if the bonding conductor satisfies 543 (adiabatic adequacy etc.) and if the (any?) PEN in the supply has a CSA no greater than 35mm², how else are you going to interpret the regs in terms of what they actually say?Do you really think that nearly all Main Earthing conductors could be changed to 10mm² and if so why?
You tell me. In terms of what is actually written in the regs I've mentioned, and any other potentially relevant regs I can think of, I can't see how else to interpret the regs - can you?In other words, do you really think your interpretation - which I do not recall having seen anywhere else nor can find any agreement anywhere - is correct or could it be counteracted by a more obscure part of a different regulation.
Sorry No, I was neither correcting nor approving what either of you had said I was merely attempting to point out that it seems that the DNO etc has the final say in what the want us to have in place and that could be over and above what the regs state.Yes, many of us remember![]()
However, you now seem to be talking/writing in what I might uncharitably describe as 'riddles' - does what you've just written (about my post you quoted) mean that EFLI and/or I "got it right" and/or "got it wrong"?![]()
Right, so I had exactly the same thoughts over a decade agoWell I never; just found this (which I don't remember).
Yes, we've always acknowledge that they have their own 'rules', and work to different regs (which may differ from regs in BS7671) - which I suppose is their prerogative.Sorry No, I was neither correcting nor approving what either of you had said I was merely attempting to point out that it seems that the DNO etc has the final say in what the want us to have in place and that could be over and above what the regs state.