Hi,
I have some questions that have been bugging me and I was hoping you'd be able to help
1.) So let's say we have a 100A main fuse (incommer fuse?) which goes to an 80A RCD in a comsumer unit, feeding 2 x 32A, 1 x 40A and 2 x 6A MCB's.
As I understand it, RCD's do not offer overcurrent protection, therefore surely it's possible under full load conditions to draw more than 80A through the RCD, causing damage? Why is there no 'MCB' type device to protect the RCD, or would the protection come in the form of downrating the incommer fuse to the rating of the RCD, in this case 80A?
2.) Around the house, we have a few 'socket doublers', those cube things that let you plug two 13A plugs in to one socket. These socket doublers aren't fused, however it is written on them that the maximum load is 13A. But what's to stop someone from plugging in two high draw appliances, causing it to overheat / melt? I'd imagine these are now illegal, and that I should dispose of them?
3.) Ring and radial circuits. We all know the purpose of an MCB is to protect the cable. So if we have a 2.5mm ring circuit with I dunno, 10 double sockets on it. Under perfect installation conditions, the cable current capacity is 27A (afaik?). This ring circuit is protected by a 32A MCB.
We plug in two heaters that draw 13A each, creating a 26A load on the circuit. The MCB 'sees' a 26A draw, however due to the ring configuration the load is 'divided' along both legs and so each leg 'sees' 13A, far below its safe maximum current carrying capacity. Great. If we then plug in another 13A heater, we create a 39A load, causing a 19.5A draw on both legs of the 2.5mm cable and tripping the 32A MCB. The circuit is protected from overload. Please correct me if I'm wrong so far!!
So I think I understand ring circuits. What if we remove the final socket 'return' leg of the ring circuit, creating a 'radial' circuit? Assuming we have two 13A heaters plugged in to the final socket, we're creating a 26A draw on the single 2.5mm feed which would be far too close to the maximum cable rating. If we then plug in an additional 5A load, we're pulling 31A through the 2.5mm cable, and the MCB still hasn't tripped.
How is this safe? Or am I totally confused?
Thanks in advance
I have some questions that have been bugging me and I was hoping you'd be able to help
1.) So let's say we have a 100A main fuse (incommer fuse?) which goes to an 80A RCD in a comsumer unit, feeding 2 x 32A, 1 x 40A and 2 x 6A MCB's.
As I understand it, RCD's do not offer overcurrent protection, therefore surely it's possible under full load conditions to draw more than 80A through the RCD, causing damage? Why is there no 'MCB' type device to protect the RCD, or would the protection come in the form of downrating the incommer fuse to the rating of the RCD, in this case 80A?
2.) Around the house, we have a few 'socket doublers', those cube things that let you plug two 13A plugs in to one socket. These socket doublers aren't fused, however it is written on them that the maximum load is 13A. But what's to stop someone from plugging in two high draw appliances, causing it to overheat / melt? I'd imagine these are now illegal, and that I should dispose of them?
3.) Ring and radial circuits. We all know the purpose of an MCB is to protect the cable. So if we have a 2.5mm ring circuit with I dunno, 10 double sockets on it. Under perfect installation conditions, the cable current capacity is 27A (afaik?). This ring circuit is protected by a 32A MCB.
We plug in two heaters that draw 13A each, creating a 26A load on the circuit. The MCB 'sees' a 26A draw, however due to the ring configuration the load is 'divided' along both legs and so each leg 'sees' 13A, far below its safe maximum current carrying capacity. Great. If we then plug in another 13A heater, we create a 39A load, causing a 19.5A draw on both legs of the 2.5mm cable and tripping the 32A MCB. The circuit is protected from overload. Please correct me if I'm wrong so far!!
So I think I understand ring circuits. What if we remove the final socket 'return' leg of the ring circuit, creating a 'radial' circuit? Assuming we have two 13A heaters plugged in to the final socket, we're creating a 26A draw on the single 2.5mm feed which would be far too close to the maximum cable rating. If we then plug in an additional 5A load, we're pulling 31A through the 2.5mm cable, and the MCB still hasn't tripped.
How is this safe? Or am I totally confused?
Thanks in advance