Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.
hi
ive got one electric shower 9.5kw and the feed runs all way to fuse box big cable 30amp fuse, can i add a 8.5kw electric shower to this or will it require sep feed and fuse
any help much aprec
you should run it in 10mm to allow for any future expansion with a 40A MCB and 30ma RCD Protection,You possibly could get away with 6mm cable but it depends on length and route of run so best stick with 10mm. You may have to get a seperate wee consumer unit ( 2 Way ) if you dont have a modern fuseboard with RCD protection or have ran out of spare ways
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local