Advice - First Fix Ring main or Radial?

I don't mind a ring final circuit but diyers dont know how to add to them properly....anyone (ish) can add to a radial circuit
 
Well, its obvious. If you want to plug the same load into the sockets. (for example a kitchen). Then a radial will either need to be 4 or 6mm .... And as an the op is more of a DIYer, its a bit silly to have to buy one real of 4mm when you can use 2.5mm on a ring.
Indeed - but if one was only installing 32A Method C radials, one would only need to buy 4mm² cable. As I've said before, if the only possible installation methods would require 6mm for a radial, I probably would revert to a ring, since (unlike 4mm²), 6mm² T+E is not so easy to use with (and a problem to get three dictators into a terminal for branches).
I'm sure you investigated 4mm prices in the past, and they weren't good value either, as not a common use
It obviously depends upon the topology of the circuit, but the cable for a 4mm² radial will often cost much the same as, and sometimes less than, that for a 2.5mm² ring. Current TLC prices (excluding VAT) are £40 for a 50m reel of 2.5mm and £35.25 for a 25m reel of 4mm. Hence, in the simplest hypothetical case of sockets arranged in a straight line radiating from the CU, with the furthest socket 25m from CU, it would cost about 13% more (in cable) to have a 2.5mm² ring than a 4mm² radial.
 
I don't mind a ring final circuit but diyers dont know how to add to them properly....anyone (ish) can add to a radial circuit
A valid point - but I'm not convinced that DIYers with the degree of knowledge you're talking about would necessarily always use the correct size cable when 'adding to' a 32A radial!

There is a 'saving grace', although I suppose I shouldn't mention it - since it flies flagrantly in the face of the regs! .... I would suggest that the reality is that it is exceedingly unlikley that a domestic 32A radial wired (in part or all) with 2.5mm² would ever result in any problems - given that it would be very rare that such a circuit would ever be asked to carry more than 27A (or, probably, more than 20A or so) in total for appreciable periods of time!
 
A valid point - but I'm not convinced that DIYers with the degree of knowledge you're talking about would necessarily always use the correct size cable when 'adding to' a 32A radial!

There is a 'saving grace', although I suppose I shouldn't mention it - since it flies flagrantly in the face of the regs! .... I would suggest that the reality is that it is exceedingly unlikley that a domestic 32A radial wired (in part or all) with 2.5mm² would ever result in any problems - given that it would be very rare that such a circuit would ever be asked to carry more than 27A (or, probably, more than 20A or so) in total for appreciable periods of time!
Yeah I think 2.5mm takes 32 amp easy, don't tell anyone I said that.
 
If the furthest socket is 25m away for the CU then I think that is a big old house rather than a normal/modern house.
We're obviously talking about 25m (or whatever) 'as the cable flies', which (even in a 'normal/modern' house) can sometimes equate to a much shorter distance from the distance 'as the moth (or even human) flies' (see **) - but I'm pleased to see you saying that, and I hope you might remind people of it next time eric start talking about 'maximum circuit lengths' of 106m (or even 32m) :-)

[ In the room of a house (e.g. a modern bungalow) in which there are, say, 6 sockets each on, say, 1.5m drops from above the ceiling, the cable length could well be 20m-25m just for that one room ]
 
Yeah I think 2.5mm takes 32 amp easy, don't tell anyone I said that.
If you also promise not to tell anyone I said this .... in the context of a domestic 32A radial, I might possibly even have said something similar about 1.5mm² (and maybe even 1.0mm²) cable, for the same reasons :-)

A catch is, of course, that the maximum Zs for adequate fault protection, remains 1.37Ω with a B32, regardless of the cable size. Assuming Method C and a TN-S Ze of about 0.6Ω (say about 0.8Ω maximum R1+R2), that equates to a maximum (radial circuit) cable length of only about 34m for 2.5/1.5mm² T+E, about 22m for 1.5/1.0 mm² T+E and about 18m for 1.0/1.0 mm² T+E !!
 