Hello All.
Weekend job was adding a few extra sockets to a mates house.
Before I started I did a EFLI test on the TN-S system and 'readings' were ok. After connecting up, my continuity tests were ok, (although the earth - neutral was a little higher than expected). I must apologise but I dont have the actual results to hand at the moment.
The insulation resistance tests between Neutral and Earth show a dead short. Every socket removed and all I found was some 1.5 links between sockets which I will change tomorrow, to save me any time can someone give me any advice please ? I dont see how my N-E-N-E did not show this ?? Maybe my meter, or brain, needs calibrating.
Thanks for any help or advice, as I want a few hours of the holiday to chill, not bl**dy work for mates rates.
Thanks Again
Ed
Weekend job was adding a few extra sockets to a mates house.
Before I started I did a EFLI test on the TN-S system and 'readings' were ok. After connecting up, my continuity tests were ok, (although the earth - neutral was a little higher than expected). I must apologise but I dont have the actual results to hand at the moment.
The insulation resistance tests between Neutral and Earth show a dead short. Every socket removed and all I found was some 1.5 links between sockets which I will change tomorrow, to save me any time can someone give me any advice please ? I dont see how my N-E-N-E did not show this ?? Maybe my meter, or brain, needs calibrating.